    What gauge wire?
    I am running a 60A sub panel from my 200A service entrance about 200ft to my new shed. From my shed, I am running 15A 220v about 100 feet to feed a pond aerator. What gauge should I use for the 60a subpanel and what wire to the pond aerator.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Dec 22, 2011, 08:11 PM
    If you use Aluminum conductors, then you would need 3, #1 AWG conductors and a #8 ground from the main panelboard to the secondary panelboard (based on Type UF insulation and 60(C) connections. If you use Copper then you would need 3 #3 AWG conductors and a #8 Equipment Ground.

    From the secondary panelboard, to the pond aerator again using Aluminium and the same type cable as above, you would need 4, #10 AWG conductors.

    If you were to go with Copper, then you would need 4 #12 AWG conductors.

    If either the aerator or the secondary panelboard would be continuous use circuits, then these cables sizes may change.
    Freedomeagle's Avatar
    Freedomeagle Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 22, 2011, 08:30 PM
    Thanks. Appreciate the info.

    For the 10 AWG, wouldn;'t it actually be a 10/2 with ground? It will be on a 15AMP circuit breaker and a GFCI plug at the pond. Didn't know a GFCI had room for four conductors?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 23, 2011, 03:49 AM
    Only need #10-2 plus ground to the GFI receptacle. If you use UF cable it will need to be 18 inch deep. If you use a GFI breaker to protect the entire circuit it can be 12 inch deep.

    I do not know how Don came up with #1 AL for the feeder to the shed. For a fully loaded 60 amp panel you can use #2 4 wire aluminum URD direct burial cable.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Dec 29, 2011, 09:26 PM
    "you can use #2 4 wire aluminum URD"... Not at 200 feet you can't. Don is correct. The exception would be a service feeder, but it's not a service feeder. #3 copper or # 1 alum is required.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 30, 2011, 03:56 AM
    Service feeder is not the key, Miss. Don is using incorrect values to to Vd calcs. That's how I arrived at #2, and he #1.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

Can I run 14 gauge wire off a 16 gauge wire? [ 7 Answers ]

I'm trying to hook up a light fixture in a garage. The existing fixture is connected with 16 gauge and I'm trying to run 14 to another fixture. Is that safe?

Can I connect a 10 gauge wire to a 12 gauge wire [ 5 Answers ]

I have 20 amp circuit with 12/3 wire and want to attach 10/3 wire to it. Can't this be done?

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search