    Intermatic t103 timer 30 amp breaker 10/2 romex 120 v to timer want two timed 120v
    I have a intermatic t103 timer I have a 30 amp breaker I have 10/2 romex from the breaker to the timer the timer says it is double pole single throw I want two 120 volt wired outlets from this timer it says it has a 120 volt clock it has one terminal that has the letter a on it and a white wire going to the clock it also has 4 terminals 1 threw 4 #1 having the other white wire from the clock #2 terminal seems to be the other side of switch # 1 switch # 2 seems to be independent from switch # 1 and uses terminal #3 and #4 so I have a black and a white coming in and two blacks and two whites going out how do I hook this all up ? I would think I may have to use a jumper wire to use switch #2 I think this timer was made for a 240 volt 3 wire in and two 120 volt 2 wire out does anyone know how to wire this up the way that I am trying to
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 2, 2011, 06:01 AM
    If you have a 30 Amp 120 volt feeder, you do not need a two pole clock, since you only have one circuit to control.

    You may bring the 120 volt to the clock connnect white to A terminal, and black to #1 and jumper to #3, this will feed both sets of contacts, and you can then have your two load wires connect to terminals #2 and 4.

    Since you have a 30 amp 120 volt feeder, each of the two loads must be wired for 30 amp, to include the wire and devices at the ends.
    radralph's Avatar
    radralph Posts: 8, Reputation: 0
    New Member
     
    #3

    Dec 2, 2011, 08:23 AM
    Thank you Tkrussell big help I may change a few things I have two 20 amp breaker that I was going to replace with the 30 amp breaker would it be better to run a 3 wire to the two 20 amp breakers the timer is rated at 40 amps and that would keep my out going stuff at 20 amp each ? Thanks for the help Radralph
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 2, 2011, 08:37 AM
    Yes, you can use a 3 wire cable to deliver two 120 volt circuits and use that clock to switch the two circuits.

    Then you will not need the jumper.

    I assume you have the wiring diagram for the clock.
    radralph's Avatar
    radralph Posts: 8, Reputation: 0
    New Member
     
    #5

    Dec 2, 2011, 12:23 PM
    Yes I do l thank you for the help the loads would be she black wires leaving the timer what do I do with the white wires leaving the timer would those go to the A terminal with the white wire that goes to the clock? Sorry so many questions I am electrically challenged thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 2, 2011, 12:53 PM
    I doubt the A terminal can handle 3 wires, add a short jumper from Term A and splice with a wire nut the jumper and the Line white and the two Load whites.
    radralph's Avatar
    radralph Posts: 8, Reputation: 0
    New Member
     
    #7

    Dec 2, 2011, 01:34 PM
    Thank you tKrussell will do by the way love the avatar Roger waters is touring going to be in portland sometime next year I am there!!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Dec 2, 2011, 01:55 PM
    He will be in Boston July 1 and I am on the presale list.

    I will be there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a intermatic t103 water heater timer it says it's double pole single throw [ 0 Answers ]

It's 120 volt I want to run two 1000 watt hps ballast off it will it work

Intermatic timer T104R installation? [ 1 Answers ]

Whould somebody tell me how to install the T194R timer to a water bomb 1.5 hP 15amp and another pump 1hp both used for water fall. Hanks, Vic

Wiring intermatic T104R timer [ 6 Answers ]

Hi everybody! I work as a handyman. While trying to install an intermatic t104r timer, I found that th E clock does not work. I believe I followed the diagram. Manually It works, but I do not hear the clock ticking. Is it supposed to? ...

Intermatic T103 Pool Timer [ 3 Answers ]

I have an Intermat T103 pool timer that was installed not long ago but the clock has never run. I'm sure the problem is that it is not wired properly because the two wires for the clock have no voltage across them. I need to know how to properly wire it.

Intermatic t103 timer hook up [ 1 Answers ]

Hi I just installed a Intermatic T103 timer to my water heater. It doesn't seem to be working. I hooked it up two different ways and still the timer stays still. I first hooked it up as the spec. lines 1 and 3 were my line and lines 2 and 4 were my load nothing. Than I tried because it is a 220v...


View more questions Search