    Water pump builds 60 psi but won't shut off?
    My water pump builds up to 61 psi but won't shut off. Is it the pressure switch?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Nov 27, 2011, 09:49 AM
    my water pump builds up to 61 psi but won't shut off. Is it the pressure switch?
    If the contacts in the control box aren't fused together so the pump can't shut off I would suspect the check/foot valve isn't allowing the pressure to be held and the pump just keeps on pumping, Check the valve out if the control contacts are OK. Good luck, Tom
    jdecker's Avatar
    jdecker Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 27, 2011, 10:58 AM
    Thanks ! I checked the contacts n they looked like they were fine, so I pulled the lines that ran to the shut off switch n they were plugged with rust/ sediment. Seems to be fine now!! Thanks again.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Nov 27, 2011, 11:04 AM
    My bad! In addition to the foot /check valve not allowing pressure to build I should have also had you check out the small tube that supplies the control box with pressure generated by the pump. Kudos for picking up on it. Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

1/2/HP craftsman jet shalllow well pump only pumps to 25 psi & won't shut off. [ 3 Answers ]

My pump pumps to about 25 psi & won't get any higher. Holds it's prime. PSI switch is per set to 40/60 & new. Air in tank checked around 25 when -0- psi on gage. Pump is maybe 3 years old. Thanks

Jet pump will not shut off and pressure does not pass 40 psi [ 1 Answers ]

I have a Myers jet pump with 2 lines coming out. The pump sits approx 20 feet high from the lake source with a 70 foot run to the lake. Pump kicks in at 20 and rises to 40-42 and will not shut off unless I manually do it and the pressure will hold constant at 40 until the water demand brings it...

When water is turned on Pump cycles on and off before pressure builds back up [ 5 Answers ]

Ok this is a new system Wellsaver Tank LPT-20 up right tank, and WaterAce RTS7 pump. Water Pressues is great and even with the pump cycling on and off still have great water pressure. This is my vac home and when I installed it last year it work great right out of box. The voltage...

Water pump pressure builds too high and won't cut off [ 3 Answers ]

I recently had to turn the water off to my house to replace the hot water heater. After we replaced the hot water heater, we went to turn the water back on but the pump had lost all of it's pressure. I was able to re-prime the pump and get water flowing to the house again. Problem solved, right?!...

Water psi drops to zero before pump comes on [ 1 Answers ]

I have a point with a jet pump. Cut in 40 psi - cut out 60 psi. Recently the psi drops to zero psi then kicks on a minute later. It goes up to 60 psi then turns off. Then when you use water it drops slowly to 40 psi then plummets to zero. What's up?


View more questions Search