    Comfortmaker RPJ 2 inducer fan runs constantly nothing else happens
    I have disconnected the unit at the power supply waited a few minutes and as soon as I power on inducer fan starts immediately no matter if its in heat or ac mode.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Nov 25, 2011, 06:11 PM
    Try disonnecting all thermostat wires from the furnace control. If it still runs, check for any open high limits, or flame rollout switches. If it still runs, you have a stuck inducer fan relay, or a bad control board, all depening on where the power to the fan comes from . Trace the wires back from the inducer motor and see where they go. If to an individual relay, give it a good wack with a screwdriver and see if it will stop running.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Comfortmaker RPJ Heat Exchanger blower fan and ac unit [ 61 Answers ]

I have a Comfortmaker RPJ model G-011 400050 - 08M -PD that when the power is turned on to the unit, the blower fan runs continuously and the outside AC unit runs continuously no matter what mode is set at the thermostat. (A/C or Heat). I just moved into the place and the thermostat looks like it...

COMFORTMAKER inducer fan motor runs but furnace won't WORK? [ 0 Answers ]

I have a comfortmaker gas forced air furnace that has me scratchin a bald spot in my head. When the t'stat calls for heat, the inducer fan turns on, I hear a click in the valve, but then nothing happens. Normally the pilot sparks on & immediately the burners fire up. It might be just...

Payne inducer runs constantly [ 0 Answers ]

Inducer motor running constantly with no previous codes. Diagnostic test lights igniter, runs blower, and quits leaving inducer running with no trouble codes and solid red led on Payne PG8MAA041100 Furnace. Furnace will not run normal heat or cool cycle from tstat.

Inducer runs constantly [ 8 Answers ]

Thanks for taking the time to read the post. This is a trane xr90 gas furnace. The inducer fan runs constantly. The unit will run and meet the set point on the thermostat and then shut down except for the inducer fan running. The unit will not start again unless I manually reset the pressure...

Comfortmaker GUA Furnace forced draft fan runs constantly [ 6 Answers ]

The furnace is a 1989 Comfortmaker GUA Series gas furnace with a White Rodgers Model 58E47-148 Hot Surface Ignition Module. With the burners unlit, the forced draft fan runs all the time. The LED light blinks constantly, which the information that came with the furnace says means "External...