    raj2160's Avatar
    raj2160 Posts: 29, Reputation: 1
    New Member
     
    #1

    Nov 20, 2009, 01:54 PM
    transformer for Weil Mclain EG boiler
    I'm looking for a transformer with a circuit breaker to replace a White-Rodgers 90-112 transformer/relay. I can't find the combination with a breaker so I figured I'll buy the transformer and then pop it in in the 4" X 4" backplate since the relay is not used anyway. Will the Honeywell AT150F1022 be a suitable replacement?

    Here is the specs:

    AT 150 F 1022 Tradeline. 120/208/ 240V, Conduit and Foot Mount, with Circuit Breaker. AT150F 50VA Transformer, 60HZ 24V Sec. UL Comp.
    Recog 9 IN Leads on Primary and Secondary. Conduit and Foot Mount. Circuit Breaker Button.

    Plate or panel mounted 120/208/240 Vac Transformer with 9 in. lead wires and metal end bells
    Honeywell AT150F 1022 Transformer Overview:
    Provide power to 24 Vac circuits in heating/cooling control systems. Intended for use in systems with predictable, uniform loads. Can be used in any application that does not exceed the listed ratings.
    Honeywell AT150 F1022 Transformer Features:
    • Rated at 50 VA
    • Color-coded leadwires for primary connections and screw terminals for secondary connections, fixed 1/4 inch (6 mm) male quick-connects or color-coded leadwires for both primary and secondary, are standard.
    • Meet NEC Class 2 requirements.
    • Meet Underwriters Laboratories Inc. Standard UL 1585 and are identified. Class 2 not wet, Class 3 wet.
    Honeywell AT150F1022 Transformer Specifications:
    Description Plate or panel mounted 120/208/240 Vac Transformer with 9 in. lead wires and metal end bells
    Electrical Ratings -Primary Voltage 120 Vac, 208 Vac, 240 Vac
    Electrical Ratings -Secondary Voltage 27.5 V.O.C.
    Frequency 60 Hz
    Mounting Includes 1/2 14 NPSM conduit connector and lock nut for mounting on plate or panel (not included) with 7/8 in. knockout, and feet for surface mount.
    Electrical Connections (Primary)(in.) 9 in. leadwires
    Electrical Connections (Primary)(mm) 229 mm leadwires
    Electrical Connections (Secondary)(in.) 9 in. leadwires
    Electrical Connections (Secondary)(mm) 229 mm leadwires
    Electrical Ratings -Output 24 Vac at 50 VA
    Dimensions (in.) 3 3/16 in. high x 2 3/16 in. wide x 3 5/8 in. deep
    Dimensions (mm) 81 mm high x 56 mm wide x 93 mm deep
    Temperature Ratings (F) -20 F to +105 F
    Temperature Ratings (C) -29 C to +41 C
    Approvals, Underwriters Laboratories Inc UL Listed: File no. E14881, Guide no. XOKV.
    Approvals, Canadian Standards Association Certified: File No. LR95329-18
    Includes Button for manually resetting the circuit breaker and metal end bells.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Nov 20, 2009, 04:12 PM
    If the VA rating of the previous transformer does not exceed 50, that'll do just fine. Be sure you wire the primary for the correct input voltage (most likely 120v.) and cap the unused leads.
    raj2160's Avatar
    raj2160 Posts: 29, Reputation: 1
    New Member
     
    #3

    Nov 25, 2009, 11:39 AM
    Thanks, just got it last night and it worked though it seems I have other problems to worry about. When I turned it on everything seemed fine. Connected the 24V controls and the boiler got power and came on. Got green on the low power cut off sensor. However when I jumped the t-stat wires to start the boiler; I was getting a clicking sound from the low power cut off sensor or at least in that area and then the transformer died. Continuity shows no continuity on the primary side. Any insight?

    Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 25, 2009, 01:43 PM
    Wow it seems the new transformer shorted out by the same problem that shorted out the original transformer.

    Is your boiler hot water or steam??

    Here is your basic manual.

    http://www.weil-mclain.com/en/multim...ler_manual.pdf

    Here is another manual with a bit more detail for service.

    http://www.weil-mclain.com/en/multim...ers_manual.pdf


    Control suplement for standing pilot furnaces

    http://www.weil-mclain.com/en/multim...standpilot.pdf

    Control suplement for spark ignition boilers

    http://www.weil-mclain.com/en/multim...supplement.pdf

    Complete master parts list

    http://www.weil-mclain.com/en/multim...parts_list.pdf


    Your boiler is available in many different trim forms. Hot water,steam,spark ignition,standing pilot,ETC. Without knowing exactly what you have I provided all info available for you to look through so you can pick out your system exactly as you have it.

    You will need to track down the shorted item and replace it so you do not damage any more transformers and to allow your system to be up and running. You might also place a small fuse into the wiring of the transformer so you only pop the fuse which is cheaper than replacing the transformer. A OHM meter will be your best friend in tracking down the defective/shorted part that is causing your problems.
    raj2160's Avatar
    raj2160 Posts: 29, Reputation: 1
    New Member
     
    #5

    Nov 25, 2009, 05:08 PM
    Quote Originally Posted by hvac1000 View Post
    Wow it seems the new transformer shorted out by the same problem that shorted out the original transformer.

    Is your boiler hot water or steam???

    Here is your basic manual.

    http://www.weil-mclain.com/en/multim...ler_manual.pdf

    Here is another manual with a bit more detail for service.

    http://www.weil-mclain.com/en/multim...ers_manual.pdf


    Control suplement for standing pilot furnaces

    http://www.weil-mclain.com/en/multim...standpilot.pdf

    Control suplement for spark ignition boilers

    http://www.weil-mclain.com/en/multim...supplement.pdf

    Complete master parts list

    http://www.weil-mclain.com/en/multim...parts_list.pdf


    Your boiler is available in many different trim forms. Hot water,steam,spark ignition,standing pilot,ETC. Without knowing exactly what you have I provided all info available for you to look through so you can pick out your system exactly as you have it.

    You will need to track down the shorted item and replace it so you do not damage any more transformers and to allow your system to be up and running. You might also place a small fuse into the wiring of the transformer so you only pop the fuse which is cheaper than replacing the transformer. A OHM meter will be your best friend in tracking down the defective/shorted part that is causing your problems.

    Hi Hvac1000

    My boiler is steam. Circuit diagram is the same as on on page 8 of http://www.weil-mclain.com/en/multim...standpilot.pdf. I've ohmed out thermostat, rollout tfe wires, main 24V feeds to R and C, spill switch and the short isn't obvious. I get 0.00 on the connections of the rollout TFE but that seems to be just a fuse but the wires individually show open line. I don't know how to check the low cut off sensor since it's mounted on a circuit board part # PS-802-24. It looks like I can bypass it if I connect pins 1 to 3 on the connector... would that be right? By jumpering 1 and 3, would the boiler start if I jump the t-stat wires? Should I check the hot and neutral on the primary. Should ground be connected to neutral as I get continuity when I test. On the damper control harnessl I get about 1 megaohm between black and ground. I also see about 3 ohms when looking at the fuse on the ladder diagram.

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Nov 25, 2009, 06:22 PM
    To test for a grounded component attach one leed to the one terminal on the component then place the other leed to a good ground (like the boiler jacket metal or a metal electrical box on the boiler. This way you can check each terminal one at a time.

    Since this is a steam boiler I do not recommend jumpering any control on the boiler to get it to run. Depending upon the circumstances steam can be a nasty little bugger.

    You need to perform the above style test on every device and wire that is in or attached to the boiler. Hopefully you will find a short circuit to ground.
    raj2160's Avatar
    raj2160 Posts: 29, Reputation: 1
    New Member
     
    #7

    Nov 29, 2009, 10:06 PM
    Thanks,

    Worked like a charm. Boiler is up and running. Was indeed a short to ground.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Nov 30, 2009, 12:11 AM
    Good deal you got heat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Weil Mclain Ultra II 230 Boiler [ 25 Answers ]

I am considering a Ultra 230 boiler and in looking over the documentation I have three questions: 1. What the heck is a "condensing" boiler? 2. Will this boiler system work with cast iron radiators? 3. The piping diagram shows a 12" long connection atop the boiler between the input and...

Weil-mclain boiler cg series won't fire up [ 2 Answers ]

Pilot stays on zones open up after thermostat calls for heat but boiler don't fire up what could it be. Any ideas? Txs.

How do I replace a wet pack / Liner in my weil Mclain boiler [ 0 Answers ]

I have a Weil Mclaine boiler. I brush it out annually then pull the burner and sweep out the debris that falls into the fire box. Each year the liner (wet pack) has more areas of thinning or concern. I found the replacement part numbers but how do I install the pack? Do I simply wet it and place...

Weil McLain Gas Heat & Hot Water Boiler [ 1 Answers ]

What does error code E-19 mean?

Weil-McLain Boiler settings? Look right? [ 3 Answers ]

Weil-McLain Gold Oil Model: WTGO-4 Series: 3 Net Output... Water 128 MBH Pressure set at 22 Water Temp at 162 Feet H20 at 40 Water Heater is Amtrol Boilermate WH7ZDW


View more questions Search