    Need help determining the right size backup generator/inverter
    I am looking to buy a backup generator (actually an inverter) for my house in case of a power outage. I am considering a Yamaha EF2000iS, but before I buy it I want to make sure it will be strong enough to meet my needs. My plan is to run the following items in case of an outage: REFRIGERATOR (KitchenAid KBFS25E) with a rating of 7.1 amps at 115 volts; 2 LIGHTS at 60 watts each; LAPTOP COMPUTER (Sony VAIO). I believe the generator/invertor can handle the load since it can rated 1600 watts continuous and peak load of 2000 watts. Before I buy it, however, I'd like to hear from an expert or someone with experience to confirm. The only issue is I'm not sure what is the startup wattage specification for the refrigerator. Thank you in advance for your help
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 6, 2011, 09:41 AM
    The issue as you sated is the starting current needed for the frig. Thou it will be for a very short time, refrigeration units have a high starting current, can be 6 to 10 times the running current.

    So, I hesitate to confirm this 2 KVA inverter will serve the frig reliably.

    Can you check with the manufacturer or dealer?

    May be good to get the starting current specs of the frig.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Use inverter to increase power output of a generator [ 7 Answers ]

Hello does anyone know if it is practical or even possible to amplify the power of a small generator using a large watt inverter? Say you have a 2 or 3 HP 1000 watt generator and you hook it up to a 5000 watt inverter. What kind of power will you be NOW able to generate? Doesn't the horse power of...

What are emergency power backup & generator synchronization requirements for hospital [ 4 Answers ]

"What are the emergency power back up requirements & Generator synchronization requirements for a hospital requirements as per NFPA 70 & CIBSE.

400amp/2-220amp grounding w/backup generator [ 1 Answers ]

I am installing a 400A. Service which will split into 2-200A panels. One will service a workshop and another will service our home. Each will have a service disconnect prior to the individual panels. The home has a 18kW backup generator. My questions are: How are the neutrals and grounds to be...

Determining breaker size. [ 2 Answers ]

How do I determine breaker(amps) size for each circuit?

Determining Belt size [ 1 Answers ]

I have changed pulley sized and now I need a new belt... how do I find out belt length?


View more questions Search