    What is a super neutral, and when is it used?
    What is a super neutral, and when is it used?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 30, 2011, 09:32 AM
    A super neutral is usually a larger neutral, 200% larger that the branch circuit rating, in a multi-wire branch circuit feeder, widely used to serve modular furniture in offices, as one example.

    The purpose is to deal with the harmonics that can accumulate on a neutral for 120 volt loads such as desk top computers, etc.
    mwcherry22's Avatar
    mwcherry22 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 7, 2011, 12:26 PM
    Comment on tkrussell's post
    Thank you very much, this is very helpful.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do single pole breakers hook black to breaker and neutral & grd to bonded neutral bar [ 6 Answers ]

I have an Eaton Cutler-Hammer meter/breaker box. (MB816B200BTS-FLCH) I want to run a 20 amp circuit (underground wire) from this box through existing underground conduit to a receptacle for a dishwasher. This run would be app. 15' to 20' and from my main house panel it would be 40' to 50'. All...

Mains neutral and generator neutral [ 0 Answers ]

I'm certainly not an electrician but one of expert around this web can help. I recently come across the problem where the ground volts raised up to 12 volts and UPS system (10KVA) was stopped working due to ground issue. Some electricians came but unable to find the actual cause then I ask from...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

Super Shy in a Super Social environment [ 8 Answers ]

I am an 18 year old, Canadian Boy My problem is that I am a very shy person when it comes to speaking with adults, strangers, authorities, and for the most part all girls. The type of people I surround myself with are the so called popular group. Having all my friends in the popular group leaves...


View more questions Search