    My central air blower will come on for heat but not ac
    My central air unit outside comes on from thermostat control but the blower will not kick on.Will not kick on even if I turn the fan on manually from thermostat. If I turn on the furnace control the blower works fine.I just replaced thermostat hoping this will fix problem, but didn't.I have to go down to the basement and turn it on and off from a switch in the unit itself.Please help! I'm burning up.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #2

    May 13, 2011, 10:57 PM
    Your fan relay is bad or the t-stat. Probably the fan relay. It's a $5.00 part and one of the fan wires leads to it. You must have a gas heater where the fan is controlled by a separate fan switch. You have two wires with 24 volts to coil on fan relay and one wire connected on normally open contact to high speed on fan, one on normally closed leading to fan switch, and one to L1 power supply. It's very simple, but don't mix them up. The symbol for normally closed is a set of contacts with a line through the contacts and no line on normally open contacts. Just look in control box in furnace where all wires lead. Most likely it is the only relay there. DrTom4444
    santoro1956's Avatar
    santoro1956 Posts: 1, Reputation: 1
    New Member
     
    #3

    May 14, 2011, 07:16 AM

    How do you replace the fan relay on the air unit
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #4

    May 14, 2011, 08:19 AM
    I need to know what kind of unit you have on the inside and how it is set up. It could be in several places. You may IM me at drtom4444 on Yahoo Messenger and you may do a video call, as well. Then I can instruct you. DrTom4444
    diyman2011's Avatar
    diyman2011 Posts: 2, Reputation: 1
    New Member
     
    #5

    May 15, 2011, 12:31 AM
    Comment on drtom4444's post
    Thanks drtom. This was very helpful. It turns out that the relay slipped out of the socket apparently from years of vibration. I simply pushed it back in and works fine. Thanks again.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #6

    May 16, 2011, 06:06 AM
    You are welcome. Glad to be a help to you. DrTom4444

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My central heat and air unit is blowing cold air. The fan cycles on and off but no he [ 3 Answers ]

My central heat and air unit is blowing cold air. The fan cycles on and off but no heat. Really cold today

Central air blower is running but no air comes from the vents [ 9 Answers ]

I hae central heating and air, when I turn on the AC with the thermostat it will blow cool air for a short time then slows to no air at all coming from the floor vents. The compressor is still spinning outside and the blower on the inside unit is blowing, but its like no air get through, any...

Central air blower working for hot air but not ac? [ 1 Answers ]

Hi, When my blower for my heat/ac is working fine when I have it on heat (from the furnace) but when I switched the thermostat over to cool the cool air came out but wasn't forced i.e. the blower doesn't start up? Any ideas anyone? Thanks a lot.:confused:

Should I choose central air/heat or ductless air/heat systems [ 7 Answers ]

Hello. I am rehabbing a house which is approx 3100 sq ft including basement. It currently has radiators and no central air. I've been reading about the ductless heating and air systems and the idea of them seem great but are they really better than the forced heat and central air systems? Is the...


View more questions Search