    How do I run 4 MC wires through a stud?
    I am running 4 new circuits and I am using MC wire as this is a commercial space and the building inspector requires MC. I am very good with electrical but had a thought whether this is allowed:
    Can I take a notch in each of the studs in the wall (11 foot wall) to fit the 4 wires? Or do I need to drill holes in the center of the studs? If Holes how many 4 - one each or can I combine wires into 2 or even 1 larger hole?

    BTW the wires I am running are 2- 12/3, 1-12/2 and 1-6/3 (for a commercial oven)

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 23, 2011, 05:24 AM
    You can check with your local building inspector, I believe notching will not be acceptable.

    All electricians do is drill one hole for each cable, spaced a few inches from each so not to compromise the strength of the stud.

    The cable needs to be at least 1.25 inch away from the nailing surface(s) of the framining member. If drywall will be on both sides, does not leave much room.

    Protective nail plates may be needed to prevent any nails or screws from being driven into the cables.
    Tenpenny's Avatar
    Tenpenny Posts: 5, Reputation: 1
    New Member
     
    #3

    Mar 24, 2011, 06:08 AM
    Thank You tkrussell!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Mar 24, 2011, 03:42 PM

    Drilling a hole in the center is much better/stronger then notching.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you run 14AWG wires off a 12AWG line? [ 8 Answers ]

I just bought a new house and was repairing a broken wire that I found in the basement. The broken wire was 12AWG and runs directly off a 20amp breaker. When I opened the junction box, I found that, the 12AWG line splits into two other lines (one goes to a light in the basement, and one goes...

Burnt wires at the Run Capacitor [ 1 Answers ]

I noticed their was no hot air coming through my vents I checked the run capacitor and noticed the wires where burnt off one prong so I spliced the and reconnected. That worked fine for a week or so , this time two wires where burnt so I repeated the process and automatically the connection started...

How do I run speaker wires in-wall in finished basement? [ 3 Answers ]

I'm finishing my basement and at the point where I need to get the speaker wiring in. I'm confused about if I need to make home runs with all the wires or just connect them all in parallel. I'll have a TV and receiver in one room and in the other room I'll have the stereo receiver. I'd like to play...

How do I run all my wires to a single breaker [ 3 Answers ]

I am building a portable hunting cabin that will be used as a rv. It will be fully equipped with a 4.6 cubit foot refrigerator, a 5.9 freezer, a 2.5 gallon hot water water heater, and a 5000btu window a/c, 2 shop lights. It will have 4 outlets total, should I use a 30 or 50 amp breaker, and where...

1.5 harness need to run what wires for 1.6 motor [ 1 Answers ]

I'm having probs because I had the d15 motor on my honda civic and now I got a d16a6 motor but I don't havethe harness to be able to run the mpfi I have the dizzy but I don't know what wires to run to activate this with the stock 1.5 harness please help... thanx


View more questions Search