    Heater fan running continuously
    My heater fan will not shut off. Pulled thermostat off the wall and fan continues to run. Any answers are gratefully appreciated. So, update: We pulled the red wire off thermostat, and fan still keeps running. The only way to shut it off is at the furnace itself. But that turns whole system down. Now what?
    smithma's Avatar
    smithma Posts: 3, Reputation: 1
    New Member
     
    #2

    Feb 23, 2011, 09:06 AM
    The air handler is usually controlled by a thermostat (or simple timer) within the unit when in heat mode. The room thermostat calls for heat, the air handler gets warm (either by hot water loop, fuel burning, or electric) then when it is warm enough, the blower is switched on. This prevents cold air being pumped into the room. The blower stays on until the heating shuts off and the air handler cools down to below the preset limit (thus extracting the remaining heat in the unit).
    My guess would be that the internal thermostat (or timer) in the air handler is stuck on.Unless you also have a humidistat connected to your air-handler and it is trying to add humidity to the room which some do must by blowing the air past a wet surface. If the water is off, the surface is clogged, the humistat is set too high, or you just have really dry air, then the unit doesn't know any different and it just keeps running without effect.
    candichristi's Avatar
    candichristi Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 23, 2011, 10:37 AM
    Comment on smithma's post
    We do not have a humidstat connected. We have no problem getting heat. After the desired temp of thermostat is met the heat shuts off and the fan continues to run blowing air with no heat. When the temperature drops from the cool air blowing then the heat kicks back on again and warm air comes out of the vents.
    smithma's Avatar
    smithma Posts: 3, Reputation: 1
    New Member
     
    #4

    Feb 23, 2011, 01:12 PM
    Comment on smithma's post
    For clarification, the thermostat I mentioned is internal to the air handler and not the one on your wall. It might be simple temperature sensitive switch mounted on the hot surface. It might just be stuck, give it a wrap.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Honeywell CT3200 - fan continuously running [ 2 Answers ]

I just noticed that regardless of whether the FAN switch is in the AUTO or ON position, the fan is continuously running. It just started to do this, this past week, up until now it was fine, only running when the furnace kicked in. When I turn the SYSTEM switch from HEAT or COOL to OFF, it...

Water Heater Exhaust Fan Running Continuously [ 0 Answers ]

I have a problem with my Kenmore power vent gas water heater: 40 Gal. Power Miser 8 and the model number is 409.737945. The problem is that the exhaust fan has been running continuously for two days, even the gas burner is off. I have checked the air pressure switch it seems okay. What else...

Continuously running fan on "Auto" on thermostat [ 1 Answers ]

The fan on the thermostat continuously runs, even if it's set on "auto". I have to shut off the main switch in order for it to shut off. But once the air kicks on, the fan stays on until I flip the main switch again. Also, the error code on the main board reads Reversed 115 VAC polarity... any...

The fan from my heater will not stop running [ 1 Answers ]

The fan from my heater will not stop running

The fan from my heater will not stop running [ 3 Answers ]

Hello, I came home this pm and my heater was running nonstop. I have changed the thermostat, but the fan will not stop running. The only way to make it stop is to turn of the breaker outside. It is a AR36-1


View more questions Search