    How can I calculate maximum demand load from connected load in KW
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 23, 2011, 07:18 AM

    Apply the proper derating factors to the connected load.

    If you list and describe the connected loads, perhaps we can help further.

    As an engineer, it is up to you to determine what loads will be energized at the same time to arrive at the demand load.
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #3

    Jan 27, 2011, 05:10 AM
    Plot a graph with time in X axis and Current or VA in Y axis at 15minute intervals and see.
    More useful method is to connect a data logger/power analyser to the main CB and record I,V,pf,Hz,VA,W,VAR, harmonics etc for a 24hr period.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 27, 2011, 09:18 AM
    Data loggers only work if the building is already built and in operation.

    A graph may work if the engineer consults with the end user to determine how the loads will be utilized.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How can I calculate maximum demand load from connected load in KW [ 3 Answers ]

Hi I am ssaha, I want to ask, how can I calculate maximum demand load from connected load? Suppose in a shopping complex cannected load is 5000 KW. Only connected load is known but other component like demand factor not specified. In that case how can I calculate maximum demand load? Please help me.

How do you calculate the maximum load created by devices on a main service panel? [ 2 Answers ]

200 amp panel is full, I need to add more equipment. When do I reach a point where I need to increase the size of the panel?

How do you calculate maximum load? [ 0 Answers ]

Suppose a machine that moves a load at 3 ft/s has a maximum power rating of 50 hp. What is the maximum load/

How can we calculate maximum demand ? [ 1 Answers ]

I want total theory of maximum demand,how it is calculated?