    200 or 400 amp service?
    We are building a new 5,400 sq. ft. home. We did the calculations for our ungrounded service entrance and learned that we need a 224 amp panel. The next typical service size available from our electric company that is larger than 200 amp is a 400 amp service. Our distance from the meter to the house is 350 feet. We have 1/0 AL run to house already for temporary construction power. What size service do we actually need? And if it is a 400 amp service, do we need to increase our conductor size? Thank you very much for your expertise. Frank Page
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 20, 2011, 06:30 PM
    Frank, I can only assume an electrician is going to be doing this work. They will have all the knowledge to do this job.

    Well, if a load cal was done, and it came in at over 200A then you DO need to go to a 400A service.

    Just so you know, yes, you do need to replace the wire, big time.
    350 feet is also too far for standard size wire. You will either need the transformer moved closer to the house or upsize the secondary service lateral conductors.


    5,400 sq/ft?? Must be nice.
    Professional athlete or corporate lawyer?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Converting from 200 Amp to 400 Amp service-Need some advice [ 0 Answers ]

Currently have 200 amp meter, 200 amp breaker disconnect (main service panel), and a 200 amp subpanel in a Manufactured home. I want to upgrate to 400 amp meter to service the home and a new shop with 200 amp. I have talked with the utility and local electrician and electrican engineers, but I...

400 amp service into (2) 200 amp panels [ 0 Answers ]

I have a job I'm looking at which has an existing 400 amp service which splits at the meter to (2) 200 amp fused disconnects and then feeds (2) 200 amp panels independently that are ion the second floor in the middle of the building. They want a 80kw generator to do the whole service with a 400 amp...

Relocating and upgrading my 200 amp service to 400 amp service [ 4 Answers ]

Im getting ready to upgrade and relocate my 200 amp service to a 400 amp service about 10 feet away away from original location. A new 400 amp meter base will be back to back with 2 new 200 amp panels. My question is, can I take out the guts out of my 200 amp panel and use it as a junction box to...

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...


View more questions Search