    Disconnect and leave wire in breaker panel to be used later
    I installed a gas furnace and want to use the old furnace circuit, how do I disconnect the furnace wire correctly to leave in the panel for future use?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jan 20, 2011, 04:55 AM

    Turn off main circuit breaker, remove panel front cover.

    Disconnect wires. If this was a 120V circuit, the black wire will be connected to the circuit breaker and the white will be connected to the neutral buss. If this was a 240V circuit both wires will be connected to the circuit breaker.

    Put a wire nut on the end of each wire and tuck out of the way. Put front panel back in place. Turn main breaker on.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

How to run 4 wire from disconnect to electrical panel [ 11 Answers ]

I am installing a new 100 amp panel. Where the se cable enters house if further then 3 ft. I am going to use a 100 amp disconnect then run wire from disconnect to panel. My inspector says I must run 3 wire to disconnect then use 4 wire from disconnect to the panel and isolate the neutral bar and...

How many feet of wire between main breaker and meter base without a disconnect [ 1 Answers ]

What is the code for the length of wire between the panel box and meter base without installing a disconnect

In a spa installation does the GFI breaker go in the disconnect box or main panel? [ 2 Answers ]

In a spa installation does the GFI breaker go in the disconnect box or main panel?

Identifying this wire size in my breaker panel? [ 5 Answers ]

The wire running to the main breaker in my panel has the following written on the side of the wire. I am trying to figure out what gauge it is. The wire says, "GENERAL CABLE 3 TYPE THW 600V MTW GUARDIANT 090 3 MACHINE TOOL WIRE OIL RESISTANT 60 C" Thanks ahead of time.


View more questions Search