    208 source for high current 120v application
    I need to power up 4, 2kW, 120v lamps. The application is to heat something up. There will be 2 lamps on top (in a reflector) and 2 on the bottom. Driven by Eurotherm controllers through SSRs. In one reflector with 2 lamps, can I run 1 leg of 208 to each lamp and connect the other end of the lamp to neutral? I don't want to run 4 each 20 amp 120v circuits, just 1, 40 amp(?? ) 208v circuit. 8kW/208=38amps, should I size the breaker at 50amps?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 11, 2011, 09:56 AM

    I do not see how a 208 Volt 40 amp feeder will solve your problem trying to feed 4- 120 volt 2kW lamps, each will draw 16.6 amps each.

    Your dealing with 120 volt loads, which needs one leg of a 208 volt system, plus the neutral, to deliver 120 volts.

    You need 4- 120 volt circuits, and technically, if they will run more than 3 hours, because the load amps will exceed 80% of a 20 amp circuit by 0.666 amps, you would need to run 30 amp rated circuits.
    RustyFairmount's Avatar
    RustyFairmount Posts: 165, Reputation: 40
    Junior Member
     
    #3

    Jan 11, 2011, 10:18 PM
    The math works, but my concern would be the gauge of wire you use. Consider that 240v is just two phases of 120v in a single package. Right? If you bond all lamps to the same neutral wire, will the neutral be a sufficient gauge to carry that much current?? We're talking 70amps of current on a single neutral line. 8000w/120v. I don't have a code book handy, but that's a beefy wire.

    Rodneyco88's Avatar
    Rodneyco88 Posts: 2, Reputation: 1
    New Member
     
    #4

    Jan 12, 2011, 10:59 AM
    Comment on RustyFairmount's post
    I believe that because the 2 hot legs are out of phase by 120 degrees that the neutral does not need to be bigger than the hot. Can someone who really knows please confirm. Thanks
    RustyFairmount's Avatar
    RustyFairmount Posts: 165, Reputation: 40
    Junior Member
     
    #5

    Jan 12, 2011, 07:53 PM
    Comment on RustyFairmount's post
    Good point on the phase.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Producing 120v but no current... [ 2 Answers ]

I have an Onan gen set that is producing 120v but when I put a load on it isn't producing current. It is a 3ph in a "Y" configuration 120v/240v When running with the breaker is off it shows 120v on all 3 legs to ground. When I turn the breaker on it drops to about 60v the more lights and...

120V heater tape off a 240V source. [ 3 Answers ]

Hi, My question is very similar to HandyJohn's and much my question was answered in is post. Mostly verifying my suspicion of needing a step down transformer here. Just wondering if you know of any simpler options I may be overlooking outside of running a dedicated line. Here's my...

Wiring 120V light from 240V source [ 6 Answers ]

I currently have a well house that has a 240V source on 12-2 wire powering a submersible well pump. I would like to wire in a 120V light. Can this be done using the 12-2 wire already in place or do I need to remove the 12-2 wire and install 12-3 wire? (It is approximately 60ft from the main house...


View more questions Search