208 source for high current 120v application
I need to power up 4, 2kW, 120v lamps. The application is to heat something up. There will be 2 lamps on top (in a reflector) and 2 on the bottom. Driven by Eurotherm controllers through SSRs. In one reflector with 2 lamps, can I run 1 leg of 208 to each lamp and connect the other end of the lamp to neutral? I don't want to run 4 each 20 amp 120v circuits, just 1, 40 amp(?? ) 208v circuit. 8kW/208=38amps, should I size the breaker at 50amps?
Comment on RustyFairmount's post
I believe that because the 2 hot legs are out of phase by 120 degrees that the neutral does not need to be bigger than the hot. Can someone who really knows please confirm. Thanks