    600v 100amps, how many amps at 240v
    How many amps are the maximum amount of amps can get from 600v 100amp service down to 240v? Thanks have a good day.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jan 3, 2011, 01:15 PM

    You need to explain yourself better.

    Please tell us exactly what you are doing.

    Normal residential service is 240 VAC and the minimum now set by the NEC is 100 amps.
    koronto's Avatar
    koronto Posts: 5, Reputation: 1
    New Member
     
    #3

    Jan 3, 2011, 01:22 PM
    I thought I would. An industrial unit has a power 600volt 100amp service. I thought I was not going to have enough power in the place. But I was told there would be more then 100amps if dropped to 240volts. How many amps at 240 dropped from 600 , I guess is the question
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 3, 2011, 02:05 PM

    Roughly 250A at 240v single-phase from 600V-100A single-phase.

    OK, that's out of the way. There is still a lot we don't know. I imagine a 600V service is 3-phase. Is the 240v service going to be 3-phase or single phase?

    What is this for?
    Is this a space you will be renting? Buying?

    NONE of this is DIY type work, I hope this is not anything you plan on doing yourself.
    koronto's Avatar
    koronto Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 3, 2011, 02:21 PM
    Comment on stanfortyman's post
    Leasing for 3years, heaters, converyor, spot dryer. Definitely not going to be doing this work myself. Can there be more amps at three phase/240? Thanks have a great day.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jan 3, 2011, 02:31 PM

    No, it's the same 250A, but the wattage is proportionately higher.

    100A @ 600V single-phase is 60,000 watts.
    100A @ 600V 3-phase is 103,800 watts
    103,800 watts @ 240V 3-phase is 250A.
    koronto's Avatar
    koronto Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 10, 2011, 05:37 AM
    Thank you very much that is exactly what I needed to know.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

240v transformer to 120,208,240v what wires [ 3 Answers ]

I'm replacing a 240v transformer in a split heat/cooling unit. The old trans has 4 prongs 2 load 2 line the new one has two secondary and 4 primary wires what wires do I use for primary?

How far can I run 240v 30 amps in a 10 gauge or 8 gauge line? [ 4 Answers ]

I'm supplying electric to a remote building with no other power source. The generator supplies 240v 30 amp. How far away can I keep the generator outside with a 10 gauge line connecting to a service panel? What if I use 8 gauge? The building is used infrequently and I run an air compressor a few...

What circuit breaker should I use for a 240V 1.6 amps [ 4 Answers ]

What circuit breaker should I use for a 240V 1.6 amps

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!


View more questions Search