    Need Help with Main Panel
    My setup right now is a 24 slot 200amp panel, I'm upgrading to a 200amp 40 slot panel and I'm moving the main 14 ft from end of my garage to middle of my garage. I've been told that I need some sort of a 200 amp breaker in between the meter and the main now because of the distance but I've gotten a couple of different answer's on what I can use as the in between device. Can you clarify for me what I need?
    This is what I have: Eaton Cutler-Hammer 1 Phase,40 Spaces, 40 Circ, W/Breaker 200 Amp Main Breaker Load Center
    This is what I was told to get: Eaton Cutler-Hammer 200 Amp, 4 Spaces, 8 Circuit Mobile Home Panel Rainproof, Westinghouse

    They told me to put this right below my meter. I was wondering if there was something smaller that I could get and cheaper. I don't need the extra breakers on the outside.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 2, 2011, 06:10 AM
    What you may need is something similar to this:

    Meter Mains/Breakers | Milbank Manufacturing

    Simply a meter socket with a 200 amp breaker builtin.

    Be sure to consult with your utility company, as each has their own preferences for manufacturer, specifications, etc.

    If the feeder from the meter to the panel's new location is run on the exterior of the home, and then enters into the building and immediately into the panel, a Main is not needed at the meter location.

    If the feeder is installed inside the building and runs the 14 feet, then the Main at the meter is needed.

    If the Main is located at the meter, the new 40 circuit panel does not need a Main Breaker. May have one if desired, but not required, can use a MLO, Main Lug Only, panel to save money.

    Once the Main is located at the meter, then any ground rods or use of underground metal water as an electrode, will connect to the neutral and equipment ground at the meter/main. The feeder from the meter to the panel will need to be 4 wire,2 hots, 1 neutral, and 1 equipment ground, and the neutral must be isolated at the panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub panel load size from main panel 200 amp to 100sub 350 ft [ 1 Answers ]

Wire conduit size fromm a main 200 amp panel to a 100 amp sub panel 350 ft away

What is always LIVE/HOT in main panel w/main breaker off? [ 4 Answers ]

We are going to be putting a dedicated 20A/12-2 wire receptacle in the basement for our treadmill. When we are putting in the new 20A breaker, we are concerned with what is 'live' in the service panel. I know the 2 service wires are hot before the main but is there a chance anything else may be...

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.


View more questions Search