    Tempstar DC90 will not relight?
    My Tempstar DC90 furnace will not relight after shutting off. Inside temp raises furnace shuts off. But when temp drops the furnace will not relight but the blower/fan will start up. I have shut off thermostat and furnace and restarted.It will light and run until temp set point. Board was replaced a couple months ago. I have been told it could be gas valve. Any suggestions?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Dec 19, 2010, 05:01 PM
    True it can be a gsa valve going bad but that's only a geuss. Have the burners and flame sensor been cleaned? Was the gas pressure checked? I know it sounds like a lot of question but it's a place to start.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Tempstar DC90 intake overheat [ 0 Answers ]

I have a Tempstar condensing furnace that shut down (probably) due to a flame roll out problem. I found the furnace blower running continuously with no heat. I discovered that the intake vent had partially melted/burned as well as the PVC A/C condensate drain line and electric air cleaner 120v...

Heil dc90 furnace blower motor won't stop running [ 0 Answers ]

Heil dc90 furnace blower motor won't stop running removed the thermostat totally it still runs I replaced the chip board an the motor still just runs. There is no flame i.e. no heat.

How do I relight my furnace [ 1 Answers ]

It says aire-flo on the front of it and I don't know how to light it

Heil dc90 furnace fan always on [ 1 Answers ]

I recently purchased a house with a Heil DC90 furnace. I just realized that the furnace fan never turns off. The heating is working properly and it keeps the temperature in the house just fine. However I am concerned that the fan is always on. The fan control switch on the thermostat is in the auto...

Darft Inducer Blower - Heil DC90 [ 3 Answers ]

My gas furnace worked fine until a day or so ago. Everything works OK during furnace startup, but the draft inducer motor does not turn off until the call for heat is over. The draft inducer motor shuts down the same time as the burners shut down. Is this normal? Isn't the inducer motor suppose...


View more questions Search