Ask Experts Questions for FREE Help !
Ask
    citrineaux's Avatar
    citrineaux Posts: 1, Reputation: 1
    New Member
     
    #1

    Dec 17, 2010, 10:54 AM
    Electric Base board heaters, wiring/thermostat question
    I have three rooms in a large house that do not have hot air vents so I installed electric base board heaters. The heaters I bought are Fahrenheat 96 In. Electric Baseboard Heater, and also a 72 inch and a 48 inch. I also purchased the on-unit thermostats for the units. The 96 inch and 48 inch are on the same circuit and the 72 is on its own. I roughed in the wires and have hired an electrician to finish the wiring. I used 14/2 romex wire. The question is, the electrician is refusing to do the wiring stating that the unit says that it is 22 amps, which is printed on the unit. I looked into it and the box says that the units are all under 10 amps each (96 In. Length, 240Volts, 2500 Watts, 8533 BTU/HR, 10.4 Amps, 72 In.Length 240Volts, 1500 Watts, 3413 BTU/HR, 4.1 Amps, 240Volts, 1000 Watts, 3413 BTU/HR, 4.1 Amps) it is the thermostat says 22 amps. He he right or do I need a new thermostat? Or am I completely wrong?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 17, 2010, 12:23 PM

    First, the 1500 watt heat at 240 volts should draw 6.25 amps, so seems you have a typo.

    The stat can handle 22 amps, but that does not mean the circuit needs to be rated that.

    However, in any case, your both wrong.

    The circuit with the 2500 watt and 1000 watt units totals 14.58 amps.

    Electric heat circuit rating is sized by increasing the circuit amps by 25%, so, 14.58 x 1.25 = 18.225, needs #10 wire and a 30 amp circuit breaker.

    The circuit with only the 1500 watt unit can be #14 wire and a 15 amp CB.

    1500/240=6.25 amps x 1.25=7.81 amps.

    A #14 wire for heat circuit can only carry 12 amps.

    So, you need to stop doing electrical work without consulting an electrician that knows what HE is doing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring two electric baseboard heaters to one thermostat [ 4 Answers ]

I am replacing a electric thermostat, how do I wire one thermostat for 2 baseboard heaters. There is 2 pairs of 220 leads and two separate sets of wires coming from the baseboard heaters. I think one wire from each of the heaters have to be connected to the power wires but I don't know which ones,...

Wiring a thermostat to 2 base board heaters [ 2 Answers ]

I am trying to find out how to wire a thermostat to control 2 baseboard heaters. The thermostat is a 2 pole with 2 red and 2 black wires. The heaters are 240v and 1350 watts each. The power is connected to a double 30 amp breaker, as per manufacturer, and is routed through the thermostat junction...

Wiring 240 electric baseboard heaters with 2 pole thermostat. PROBLEMS ENCOUNTERED. [ 5 Answers ]

Howdy all, I have looked at the previous postings as I frequent the site for help on subjects. I am however perplexed as to what I have done wrong. I am installing 4 electric heaters, on 2 separate 240 breakers. Each breaker is 30 AMP. I used 12/2 Red Heat resistant wire and ran the line...

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...


View more questions Search