    Goodman furnace not working
    I have a Goodman GMP100-3 furnace that will not work. This is what it is doing... The small blower at the top will switch on and start turning. The ignitor will click and start glowing bright orange, although it takes several seconds for this to start after the blower kicks on. Then nothing. The ignitor will glow for a few seconds, maybe 10, and then the system shuts down. It will not light. The burners do not go on. The LED status light will come on when this process starts, stays constant red and then turns off once the system stops. It does not blink a code. The sensor was dirty, so I cleaned it with steel wool, hoping that was it, but still nothing. The fuse looks good. I have checked everything I can. Someone suggested it might be my circuit board, but I do not know. Any suggestions?
    raven2861's Avatar
    raven2861 Posts: 1, Reputation: 1
    New Member
     
    #2

    Nov 5, 2010, 02:55 PM
    Check tte auxiliary limit, it should be closed (you should have continuity through it) also check all the rollout switches. The aux. limit is located behind the control board, there will be two purple wires leading to the limit. GOOD LUCK
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Nov 5, 2010, 05:16 PM

    The fact that the led light goes out completely makes me think the circuit board is the problem. However, I never would give you advice to replace the board without having the system tested completely by an onsite tech. Normally, if the led is off completely, it's a problem with the board, or low voltage problems.
    ncc630's Avatar
    ncc630 Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 6, 2010, 05:06 PM
    Have a goodman furnace gds 80703ana need to know wear the high limit switchs are at it keeps flahing four times I missing a high limit switch ?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace not working after turning off and back on [ 6 Answers ]

Hello, we purchased a Goodman furnace June 2006. When we turn off the furnace, and turn it back on, the furnace does not work. I've left numerous voice mail and text messages for Air Kings in Columbus, Oh and they do not return my call. This is the company that installed the furnace. It is 30...

Goodman gmp075-3 furnace not working [ 0 Answers ]

Fan does not shut off, even with thermostat disconected. Blinking code 5. Are these problems related, and how do I fix it?

Can't get my Goodman furnace working [ 3 Answers ]

I need help getting my goodman furnace working, I've changed the igniter and the pressure switch and it still isn't working. The light keeps blinking and it says on the door that it's a 115v reverse polarity, does anybody know what that means?

Goodman Gas Furnace Not Working [ 2 Answers ]

I have a Goodman Model # EG030075-1AB REVC Gas Heater it has been converted to run on LP Gas. Furnace has worked fine for years. Turned the heat on and nothing happens. The LED on the control board is not lit. I checked the voltage at the control board and all the voltages appear to be normal. ...


View more questions Search