    Hot wire in main panel
    I have a rental home that I am remodeling I had all the wiring replaced by an electrician. I noticed a 20amp breaker was tripped so I replaced it with a new one and it tripped also so I took the black 12gauge wire off the breaker and its white partner, just out of curiosity I tested the wire and found that it reads 120 even though it is removed from all power in the panel. Does anyone have any idea why the wire would be hot and what I should do next?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 9, 2009, 02:09 PM

    Its double fed, turn off breakers off one by one to locate. Then leave both breakers off and see what went out. You may find a living room circuit connecting with a bed or bath circuit.
    Fixing is tough to put in words due to the fact it is a GFI or Arc Fault breaker. Cap one black for now, as if it is on 2 breakers, wires could see 40 amps before tripping.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Jun 9, 2009, 08:06 PM
    You're lucky you didn't get zapped when you removed the wire. Although this situation is rare, it happens. Invest in a voltage tester and use it when working on any circuit.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jun 10, 2009, 04:09 AM
    I recommend that you have this electrician:

    Quote Originally Posted by dstokes6 View Post
    I had all the wiring replaced by an electrician.
    Return ASAP to correct this issue.

    He clearly made a serious mistake in splicing while he rewired the home.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Redistribution of existing 3 wire aluminum #4 50 amp line from main panel [ 1 Answers ]

How do I connect an existing 3 wire aluminum #4 line from my main panel to a sub panel that I will use to supply a 40 amp electric oven and a 20 amp circuit for a microwave. Do I connect the bare wire to the ground bar or common and do I a connect the nutral bar to the ground bar. I know how I...

Wire type from main panel to adjacent subpanel [ 1 Answers ]

I have a 200 amp main panel that is nearly full and I plan on adding a 100 amp subpanel close by in the basement of my residence (south-east PA). I happen to have some wire available that I believe is adequate gauge (based on reading many other posts) but I want to make sure the specific wire I...

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...


View more questions Search