    How do you convert 410A to 22 freon in a duraguard airhandler
    We have a 410A duroguard Air Handler that needs to be converted to R22
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 14, 2010, 03:37 PM

    You do not convert unless it was certified at the factory at the time of manufacturer that it could be used with R-410A refrigerant. R-410A runs at a higher pressure than R-22 and that is the problem.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Sep 14, 2010, 04:11 PM

    Are you saying you have a 410A airhandler now, but a 22 condenser unit outside? You can use 410 rated evap coils on a 22 system as long as you use the correct metering device. Im assuming this is a air handler replacement while keeping the old condenser unit?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Which freon is r22 are 410a what seer is best 12 r13 [ 1 Answers ]

Which freon is best to use r22 or 410a what seer is best 12 or13

Which freon is r22 are 410a what seer is best 12 r13 [ 0 Answers ]

Which freon is r22 r 410a what seer is best 12 r13

Freon 410a [ 3 Answers ]

I have installed a 4 ton Goodman 16seer unit using 410a. I tried to follow the book on this installation. Run gas through the pipes while brazing. New copper, 1 1/8 on return. Pulled a vacum to 40 micro, my hoses kept leaking so I used all copper pipe from guages to vacuam pump, 410 tank, to...

About the new 410A freon [ 2 Answers ]

Is There A Conversion Kit For My Old Gauges For Checking R22 To The New 410a?


View more questions Search