    How do you convert 410A to 22 freon in a duraguard airhandler
    We have a 410A duroguard Air Handler that needs to be converted to R22
  • Sep 14, 2010, 03:37 PM
    hvac1000

    You do not convert unless it was certified at the factory at the time of manufacturer that it could be used with R-410A refrigerant. R-410A runs at a higher pressure than R-22 and that is the problem.
  • Sep 14, 2010, 04:11 PM
    mygirlsdad77

    Are you saying you have a 410A airhandler now, but a 22 condenser unit outside? You can use 410 rated evap coils on a 22 system as long as you use the correct metering device. Im assuming this is a air handler replacement while keeping the old condenser unit?