    Parallel conductor sizing
    I have to run power to a building 1200 amps service, the building is located 1500ft from FPL transformer the voltage will be 277/480, what size wire should I use.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 9, 2010, 11:38 AM
    You should use whatever size wire your foreman or supervisor tells you to use.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 9, 2010, 01:23 PM
    1200 Amps 277/480 volt run at 1500 feet?

    Even I will not touch this.

    Seriously, this needs engineering.

    Or bring the high voltage 1450 feet, then change over to 480/277 volt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrons are emitted from a conductor when the conductor is? [ 3 Answers ]

Multi. Choose... A. exposed to weak light. B. cooled rapidly C. Bombarded by high-speed electrons D. subjected to a small voltage

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Electrical conductor [ 3 Answers ]

Is plant oil an electrical conductor.

Conductor sizing? [ 5 Answers ]

TK, Cobraguy, Labman, KISS Okay, I now have a nine volume set of current books ranging from simple wiring to the NEC. I also sound some U.S. Navy BPARS manuals and theoretical engineering books from when I went to Internal Corporate electrical schools. Not to mmention product specific...

Sizing parallel conductors [ 2 Answers ]

On a 400 amp service for a commercial building. I'm trying to figure out the conductor size using parallel runs. I think 3/0 is sufficient but not sure. 3/0 is good for 225amps under the 90 degree column. Do you then multiply by 2 for 450 amps?


View more questions Search