    200 amp service
    Building a new home. Have a 200 amp meterbase and disconnect on backer board appox. 175 feet from home. Do I run 3 wire or 4 wire to house breaker box? They have a 3 wire service cable coming out of basement breaker box to a outside junction box. I don't want the junction box. I want to direct wire it. Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 25, 2010, 01:09 PM
    The feeder from the meter/disconnect must be four wire to the panelboard.

    The three wire from the panelboard to the junction box must be removed, as the panel must be wired with the four wire feeder from the meter.

    Sounds like the panel was wired with 3 wire in assumption of having the meter with no disconnect directly on the home. I assume there is a Main Breaker currently in the panel.
    meddles1's Avatar
    meddles1 Posts: 5, Reputation: 1
    New Member
     
    #3

    Aug 25, 2010, 03:53 PM

    That is what I thought. I'm running 4 wire from disconnect to panel directly and do away with junction box on house and go directly in through wall with LP's. Does the 4 wire from disconnect to house need to be in conduit under ground or just on the "up feeds" to LP and disconnect?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

How much does it cost to change 100 amp service to 200 amp service? [ 5 Answers ]

I am buying a house with 100amp service and the home inspecter said I would need at least 150 amp panel to service the hot tub that comes with the home. However, the hot tub is hooked up to the 100amp service panel and the hot tub works fine. Am I really running into any issues here if I do...

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

Extending 200 amp service to another 200 amp panel [ 1 Answers ]

Hello Everyone, As I just found this site this is my first time posting. I am in the process of doing an addition to my home and I am having the electrical service moved as the addition is on an exterior wall. I installed a new 200 amp panel and I need to extend the electrical over to my...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search