    Air conditioning stopped working, is flooding floor, and makes bubbling noise.
    I have an issue with my a/c. I noticed yesterday that I had an excessive amount of water in and around my unit. I checked the drain and it is clean and clear. It seems as though the unit housing the A-coil is condensating excessively and the water draining from the walls of the unit is leaking around the pan along with the coils dripping into the pan. What would cause so much condensation? Could it be blower speed or low refridgerant? The unit sounds like running water/bubbling noise coming from A-coil area of the unit. Outdoor fan is running fine and voltage checks good. The air flow in the house seems to be reduced compared to before I found the water as well.
    talkinggoat's Avatar
    talkinggoat Posts: 6, Reputation: 1
    New Member
     
    #2

    Aug 17, 2010, 03:06 PM

    There is no such thing as excessive condensation, unless there is an air leak, letting moist air from outside, into your home.

    There is no way the coil can make enough condensate to overwhelm the drain line; it has to have a blockage, somewhere, maybe down the line.

    If the A/C isn't blowing as hard, check your filter. If it's OK, check the a-coil, where air is flowing into it; it's probably clogged or frozen. You can tell if it's freezing, just by looking at the tubes running through it. They should be moist, not frosty.

    Either way, more moisture, without an air leak from outside, means that the coil is running cooler than it usually does, which means low freon or restricted airflow, because the coil is freezing, and/or not getting enough air circulation across it. One of these is probably the case, as the housing shouldn't really have condensation on it.
    whyley's Avatar
    whyley Posts: 2, Reputation: 1
    New Member
     
    #3

    Aug 17, 2010, 10:10 PM

    +1 to talkinggoat! Change your filter

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My central air makes a grinding noise right before it comes on and before it goes off [ 1 Answers ]

My c/a has been running fine, but it makes a few second grinding noise right before it comes on and right before it goes off. The unit itself is only 2 years old, but my furnace is pretty old. Is this something I should be concerned about.

1991 honda accord air conditioning stopped blowing cold air [ 0 Answers ]

Is there a relation to my crappy fuel millage, no cold air blowing from my air condition, and my very erratic idle issue? Is my ecu ? Or a valve sensor?

Toilet makes rushing air noise! Help! [ 1 Answers ]

We currently live in a 5 year old home that has three bathrooms. Now, the problem persists in our Master Bath. After you use any water source in the bathroom, the toilet makes a rushing air noise (for a second or two) every 5 minutes. It subsides after about 45 minutes. I looked in the...

Air conditioning with or without table and floor fans [ 2 Answers ]

When one is trying to cool down a room with an air conditioner (not central!) is it better to run ceiling, floor and table fans or is it better for the air conditioner to work alone? I don't want to waste electric if it isn't helping me to cool the room!:p :confused:

Combustion Air Blower makes noise. [ 3 Answers ]

Hi all, I have a 4 and 1/2 year old ComfortMaker furnace. The combustion air blower started making a rumbling noise while starting and stopping and continues to vibrate while running. I had a heating & cooling service look at it. $65 just to show up. Without taking anything apart he said...


View more questions Search