Thermostats keep dying.
Recently my t-stat wouldn't respond to anything but still showed a display. I replaced it with a new honeywell T-stat and everything worked for serveral days then it compelety died. I wouldn't display anything. I checked voltage was getting 24v on red to the stat. Batteries are new and good. What could be killing the t-stats?
|
|
 |
Junior Member
|
|
Aug 14, 2010, 07:01 PM
|
|
In no particular order,
1. The thermostat may be defective.
2. The +24 line may be intermittent. Check to make sure the screw is tight and the wire if firmly in the connector.
3. The T-stat wire is solid and could be broken inside the insulation from flexing.
4. About the only thing that will permanently damage the T-stat is excessive voltage on the red wire. This problem could be caused by a fault in the AC/HP.
|
|
 |
Uber Member
|
|
Aug 14, 2010, 07:25 PM
|
|
I'm also thinking static electricity especially if the floor is carpeted or you wear clothes that may generate it.
Make sure you touch the wall first before operating the thermostat.
A fix that works a lot of times when batteries are involved is to cut power at the breaker. Remove the batteries. Short the battery terminals together for 30 sec.
Re-install and turn on.
Some stats have reset buttons that must be depressed when batteries are installed.
Loose and intermittant contacts can cause both destructive and non-destructive failures. The above may fix it.
|
|
 |
New Member
|
|
Aug 16, 2010, 07:55 AM
|
|
Ty for the suggestions but I tried all those things and have hardwood floors. The new one is comepletely dead . Could a broken or damaged wire to the stat from the unit be causing the burn ups?
|
|
 |
Uber Member
|
|
Aug 16, 2010, 09:50 AM
|
|
Yes. It could be an loose wire.
|
|
 |
Ultra Member
|
|
Aug 16, 2010, 11:07 AM
|
|
(quote) I wouldn't display anything. I checked voltage was getting 24v on red to the stat.
You said you checked the red wire and was getting 24 V ,so what wire would be broke to keep it from getting power?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Two thermostats to one
[ 3 Answers ]
Right now I have two separate thermostats, one obviously controlling the A/C (heat pump), and the other controlling a gas furnace. To save money, I've upgraded the heat thermostat to a programmable thermostat (using two wires, red and green).
I would love to have one thermostat controlling the...
Thermostats
[ 1 Answers ]
Hope there is someone that can help me out my mother lives about an hour and a half from me and I was hooking up a thermostat for her heating and cooling unit her old unit was a rheem and the new one was a honeywell and the wiring digram was totally different is there anyone out there that can tell...
Thermostats HELP
[ 2 Answers ]
Okay guys I just moved into a new place and the thermostat is way off. It's a mechanical one, so today I went out and bought a honeywell programmable one and tried to install it. The problem is the wiring which I have no clue.
What is included in the honey well is:
Y
G
W
Rc
Rh
Two Thermostats to One
[ 2 Answers ]
I currently have a separate thermostat for the heater and the A/C... I want to combine them into one thermostat... I have replaced the thermostat before, but my knowledge of the wiring is very basic... My issue is that I have two "R" wires and I am worried about combining them together since it is...
Thermostats
[ 3 Answers ]
I have recently purchase a home and I found two thermostats installed, they told me one controls de AC and heat and the other one heat only, They're located on different rooms. Can anybody tell me how can I replace this two thermostats into one? Thanks
View more questions
Search
|