Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Thermostats keep dying. (https://www.askmehelpdesk.com/showthread.php?t=498178)

  • Aug 14, 2010, 04:00 PM
    vegeta535
    Thermostats keep dying.
    Recently my t-stat wouldn't respond to anything but still showed a display. I replaced it with a new honeywell T-stat and everything worked for serveral days then it compelety died. I wouldn't display anything. I checked voltage was getting 24v on red to the stat. Batteries are new and good. What could be killing the t-stats?
  • Aug 14, 2010, 07:01 PM
    PellMell

    In no particular order,

    1. The thermostat may be defective.
    2. The +24 line may be intermittent. Check to make sure the screw is tight and the wire if firmly in the connector.
    3. The T-stat wire is solid and could be broken inside the insulation from flexing.
    4. About the only thing that will permanently damage the T-stat is excessive voltage on the red wire. This problem could be caused by a fault in the AC/HP.
  • Aug 14, 2010, 07:25 PM
    KISS

    I'm also thinking static electricity especially if the floor is carpeted or you wear clothes that may generate it.

    Make sure you touch the wall first before operating the thermostat.

    A fix that works a lot of times when batteries are involved is to cut power at the breaker. Remove the batteries. Short the battery terminals together for 30 sec.

    Re-install and turn on.

    Some stats have reset buttons that must be depressed when batteries are installed.

    Loose and intermittant contacts can cause both destructive and non-destructive failures. The above may fix it.
  • Aug 16, 2010, 07:55 AM
    vegeta535

    Ty for the suggestions but I tried all those things and have hardwood floors. The new one is comepletely dead . Could a broken or damaged wire to the stat from the unit be causing the burn ups?
  • Aug 16, 2010, 09:50 AM
    KISS

    Yes. It could be an loose wire.
  • Aug 16, 2010, 11:07 AM
    wmproop

    (quote) I wouldn't display anything. I checked voltage was getting 24v on red to the stat.

    You said you checked the red wire and was getting 24 V ,so what wire would be broke to keep it from getting power?

  • All times are GMT -7. The time now is 03:10 PM.