 |
|
|
 |
New Member
|
|
Aug 12, 2010, 07:09 AM
|
|
How many 500mcm wires for a 1000 amp service
I have a upgrade from 600amp to 1000amp service there are 2 3" conduits from breaker up to weather heads I am pretty sure I need 3 sets of 500mcm per phase can I change the 3"conduits to 4" and split up the phases in that short distance.
|
|
 |
Uber Member
|
|
Aug 12, 2010, 08:17 AM
|
|
Your pretty sure?
All conductors of a system must be run together, either bundled or in a raceway.
So, all three phase and one neutral of each set must be together.
If you have more than one set in a raceway, you may need to derate.
Assuming 4- conductors for a three phase four wire system, 500 MCM copper wire with THHN/THWN insulation, I would have three 3 inch conduit risers.
|
|
 |
Electrical & Lighting Expert
|
|
Aug 12, 2010, 12:48 PM
|
|
 Originally Posted by mr480
I have a upgrade from 600amp to 1000amp service there are 2 3" conduits from breaker up to weather heads I am pretty sure I need 3 sets of 500mcm per phase can I change the 3"conduits to 4" and split up the phases in that short distance.
I agree with TK, you are "pretty sure"? This is something I would think you would want to be certain about BEFORE doing it.
There is a lot of money at stake if it is done wrong.
Who is doing this work? You or an electrician?
|
|
 |
New Member
|
|
Aug 13, 2010, 07:48 AM
|
|
 Originally Posted by stanfortyman
I agree with TK, you are "pretty sure"? This is something I would think you would want to be certain about BEFORE doing it.
There is a lot of money at stake if it is done wrong.
Who is doing this work? You or an electrician?
Pretty sure was a figure of speech just wanted to know about running
9 500mcm's in 2 4" conduits for a lenghth of 10' from breaker to weatherhead and no there is no nuetrals coming from the power company just 3 phase 480 off of the transformer. I have 3 3" running to the station.I really don't have room in enclosure to add another 3" to the top of the can so I thought about upsizing pipe at the pole only.Waiting on specs from breaker company I may need to change enclosure size so that will fix my problem.
|
|
 |
Uber Member
|
|
Aug 13, 2010, 08:42 AM
|
|
Will each of the two 4" have 9 - #500 MCM?
For a 1000 amp you only need 3 sets of 3 - #500 MCM
Something does not make sense.
If I am reading you correctly, you have 3 - 3 inch conduits already.
Perhaps some photos of what you have will help you explain.
I still do not know what type of insulation the 500 MCM has or will have.
|
|
 |
New Member
|
|
Aug 13, 2010, 08:46 AM
|
|
 Originally Posted by tkrussell
Will each of the two 4" have 9 - #500 MCM?
For a 1000 amp you only need 3 sets of 3 - #500 MCM
Something does not make sense.
If I am reading you correctly, you have 3 - 3 inch conduits already.
Perhaps some photos of what you have will help you explain.
I still do not know what type of insulation the 500 MCM has or will have.
Thhn insulation existing is 2 3" want to change out to 2 4" because of the room put 9 total 500's in 2 4" conduits.
|
|
 |
Uber Member
|
|
Aug 13, 2010, 08:54 AM
|
|
How do you plan to split 9 - 500 MCM , which I believe is your 3 sets of three?
Keep in mind, all three legs of each set must be run together.
4 inch GRC or PVC Sch 40 can only hold 7 - #500 MCM THHN/THWN.
Be sure your "thhn" is dual rated as THHN/THWN.
Also keep in mind, that one you have more than 3 current carrying conductors in a raceway, you need to derate.
If you use 3 - 3 in rises each for 3 - #500 MCM you do not need to derate.
|
|
 |
New Member
|
|
Aug 13, 2010, 09:04 AM
|
|
We must be on a different page I know I need 3 of each phase for a 1000amp I know I cannot fit 9 wires in 2 3" conduits you can only put 4 each which leaves 1 left over therfore i will need to add a conduit but do to space I would like to replace existing 3" conduits with 4" and put 5 in one of them and 4 in the other what Ive been asking is will it hurt anything
|
|
 |
Uber Member
|
|
Aug 13, 2010, 09:09 AM
|
|
In my first post, I addressed this question
 Originally Posted by tkrussell
All conductors of a system must be run together, either bundled or in a raceway.
So, all three phase and one neutral of each set must be together.
You cannot split up the phases.
You cannot run 5 in one and 4 in the other.
You may run 6 in one conduit and 3 in the other
Conduit.
And, then, if you do run 6 in one conduit, it is more than three current carrying conductors, you must derate the 6 conductors that would be together.
|
|
 |
New Member
|
|
Aug 13, 2010, 09:12 AM
|
|
 Originally Posted by tkrussell
In my first post, I addressed this question
You cannot split up the phases.
You cannot run 5 in one and 4 in the other.
You may run 6 in one conduit and 3 in the other
conduit.
And, then, if you do run 6 in one conduit, it is more than three current carrying conductors, you must derate the 6 conductors that would be together.
Thanks that is what I was not sure of
|
|
 |
Uber Member
|
|
Aug 13, 2010, 09:13 AM
|
|
OK, now that I got my point across, can you tell me why phase conductors can not be split up?
Also, what is your background?
|
|
 |
New Member
|
|
Aug 13, 2010, 09:16 AM
|
|
 Originally Posted by tkrussell
OK, now that I got my point across, can you tell me why phase conductors can not be split up?
Also, what is your background?
Painter
|
|
 |
Uber Member
|
|
Aug 13, 2010, 12:32 PM
|
|
So I will guess that you do not know why the phase conductors cannot be split.
|
|
 |
New Member
|
|
Aug 13, 2010, 03:29 PM
|
|
 Originally Posted by tkrussell
So I will guess that you do not know why the phase conductors cannot be split.
No I don't
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How much does it cost to change 100 amp service to 200 amp service?
[ 5 Answers ]
I am buying a house with 100amp service and the home inspecter said I would need at least 150 amp panel to service the hot tub that comes with the home. However, the hot tub is hooked up to the 100amp service panel and the hot tub works fine. Am I really running into any issues here if I do...
Relocating and upgrading my 200 amp service to 400 amp service
[ 4 Answers ]
Im getting ready to upgrade and relocate my 200 amp service to a 400 amp service about 10 feet away away from original location. A new 400 amp meter base will be back to back with 2 new 200 amp panels. My question is, can I take out the guts out of my 200 amp panel and use it as a junction box to...
View more questions
Search
|