    How do I wire a 30 amp receptacle with three prongs from a sub panel
    Hey Everybody!

    I am in the process of wiring a 30 amp receptacle that has only three prongs (Like an old dryer plug) for my new Miller 211 that I should be getting tomorrow. In the past I have always hooked up one black (110) to one of the lower prongs, one red 110 to the other lower prong and then the neutral to the top center prong. Now I was told that would be wrong if I am coming from a sub panel (which I am, from by attached garage to the new shop). I realize I could just go out an get one of the new four wire receptacles but it still won't work with the three prong plug that comes with the welder ( it comes with a Neme 6.50 P . Help,
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 22, 2010, 03:45 AM

    You need/have a straight 240v circuit. This requires only two hots and a ground. A dryer is a 120/240v circuit that requires a neutral.

    You can run 10/2 cable and use the black and white as your two hots and the bare is the ground. You must re-mark the white as a hot wire with a permanent marker or similar method.
    Be sure to attach the bare to the ground bar in the panel, not the neutral bar.
    rpberchtold's Avatar
    rpberchtold Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 22, 2010, 11:00 PM

    stanfortyman:

    Thanks so much for your help, I am now up and welding!

    Your Help was greatly appreciated.
    Rpb

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

3 wire to 4 wire from sub panel to receptacle [ 1 Answers ]

I am installing a new stove and running new romex from the box to the stove. How do I properly connect the 4 wires at the box that currently has only 3 wires so that the new system is grounded? Saw this above and it is similar to my question earlier, with the response being "yes" as to the box...

That intersting--60 amp sub-panel #4 or #6 wire. [ 21 Answers ]

I am getting mixed messages from different licenced electricians. Run length 100ft. 60 amp sub-panel in 1" conduit. Wire size according to NEC?? 2 electricians have stated #6 1 electrician has stated #4 I have also verbally talked with another electrician that said you have to rate the wire...

Wire needed for a 100 amp sub panel? [ 3 Answers ]

I am installing a 125 Amp Sub panel in a detached shed approximately 100' from the house. The subpanel has a 100 amp main breaker in it and I have a 100 amp breaker that will go in the main house panel to feed it. I will be using #4 copper THHN for my 2 hot conductors and neutral conductor and a #6...

100 amp sub panel wire size [ 2 Answers ]

I now have the 100 amp breaker installed in my load panel. I will run wiring from the load panel to a 100 amp sub-panel in an unground 80 schedule PVC. I believe I need to use #2 wire for the hots and the neutral. If this is correct, then what size ground do I use? Number 6? The sub- panel...


View more questions Search