    Running romex in pvc conduit
    Just bought 85 feet of romex #6/3 and 1" pvc conduit and was going to run from my house to a sub panel in my shed. Now I hear that's not the way have any sugestions?
    Guess I should have researched before buying materials.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jul 21, 2010, 05:17 PM

    Unfortunately true. You could use UF in conduit-code is not too clear on that-but Romex is not permitted.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jul 21, 2010, 06:02 PM

    The reason why MN cable is not allowed in conduit to go across a yard is because it is outside and even though the cable will be in conduit, NM is not listed for a "Wet" area. The inside of buried conduit is considered to be a wet location.

    A better solution would be to use THWN conductors.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Jul 22, 2010, 05:16 PM

    In addition to the other comments, you would need 4 wires run to that sub-panel. A ground wire must be run as well.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Romex in PVC Conduit ? [ 26 Answers ]

Need to run #12 wire to my gate opener. Have 1" schedule 80 conduit in ground. Can I run 12/2 Romex through the conduit to feed the gate ? Or do I have to run individual wires. Thank You

12/2 NM-B Romex in PVC Conduit [ 4 Answers ]

Hi. I need to bring 2 new circuits from the panel in the garage to the basement. I would like to use 12/2 NM-B (Romex with ground) from the panel through PVC conduit to the basement. It is about a 12' run, then a 90 degree turn, then about another 10' to a spot below the panel. At this point it...

Running PVC Conduit, sockets, and waterfall pumps [ 1 Answers ]

1) I am in Harris county Texas and have not found specific rules on proper depth for burying 120 line in pvc conduit. I plan to bury 18 inches to comply/exceed NEC standards. Anyone know the exact required depth? 2) When the conduit reaches the house, can it follow the foundation above ground,...

Romex in conduit [ 3 Answers ]

I have 1/2" rigid conduit, can I run 12 AWG through it for a length of about 6'? It will be a single cable pull, and it has one 90 degree bend.

Running pex under slab in pvc conduit [ 1 Answers ]

I have a 10' run of 1/2" pex I want to run under a slab that will be poured. Everything I have read says that you must use a non-metallic elbow (such as PVC) to bring the PEx up through the slab. I am running this line for an island sink supply. I would feel more comfortable if I not only ran it...


View more questions Search