    Romex in conduit
    I have 1/2" rigid conduit, can I run 12 AWG through it for a length of about 6'? It will be a single cable pull, and it has one 90 degree bend.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    May 27, 2008, 08:33 AM
    Code is mute on running NM in conduit, yet you would need to do a conduit fill calculation to see if what you are trying to install will meet code.

    Here it is in a nut shell:
    If you are just sleeving (protecting) the NM for six feet, I say go for it (recommend 3/4" conduit).<-----Note: in this case, both ends of the conduit are open. Yet, if you are running the conduit from box to box, then use THHN.
    peter030205's Avatar
    peter030205 Posts: 56, Reputation: 5
    Junior Member
     
    #3

    May 27, 2008, 12:08 PM
    Here is the situation... I have an outlet in my kitchen that is currently served with 14 awg wire, no ground (and the conduit is not grounded). I want to install a new grounded 20 amp receptacle, easiest way is to fish the wire from the basement to outlet (6' ish). The conduit will be attached to the box in the kitchen but will be open in the basement where I'll be tapping into an existing 20 amp kitchen circuit.

    If I were to run individual wires through the conduit I would then need a new junction box in the basement to tap into the romex, correct? Quicker and easier to do the romex in the conduit, but I'll do the calcs to see if I'm within code.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #4

    May 27, 2008, 05:19 PM
    You never mentioned what type of conduit. Yet, I'm going to assume it's emt. If my assumption is correct, then you should be fine with one 12-2 NM-b in 1/2 EMT conduit. "Very tight fit"! Yet, I still recommend you pull #12Thhn. To add: RNC (Sch 80) and ENT will not work . You will have to up size to 3/4".

    If I were to run individual wires through the conduit I would then need a new junction box in the basement to tap into the romex, correct?
    Yes, and the Junction box will have to be accessible.

    I want to install a new grounded 20 amp receptacle
    If you plan to install a recptacle in a kitchen, then see my post here: https://www.askmehelpdesk.com/electr...nt-219313.html

    Please note that in the forum room I listed above, it speaks on the kitchen receptacle requirements. Note: Code says no fewer than two small appliance circuits. This means you have to have two, yet it also means you can have more than the two required.



    RATE THIS ANSWER

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can romex be installed in a conduit [ 13 Answers ]

I am installing a new 100A sub-panel. The feed will be from main with a 100A dual-pole breaker. The main and the sub-panel are in the basement. The new sub-pnael Will be about 25 feet from main. I already bought the feed cable for this sub-panel. I bought #4/3 With Ground NM-B romex. The...

SEU & Romex [ 1 Answers ]

Can SEU and NMB cable be uses interchangely for a 60 amp, 240 volt circuit.

Romex to spa box [ 7 Answers ]

I am mounting a spa box on a new exterior wall. I have 6-3 +gnd romex wire running from the panel to the box. I want to bring the wire from inside the wall right into the back of the spa box. Is this okay? I have noticed some spa boxes have knock-outs on the back while others do not. If I do...

15A vs. 20A on #12 Romex [ 10 Answers ]

We are running #12 Romex wire for circuits from the panel. I want some of the breakers in the panel to be 15amp and some to be 20amp. My electrician says that they should all be 20amo because #12 Romex is code for 20 amps. I said sure but it shouldn't matter is we go smaller than code (i.e....

Bx or romex 240 or 120 [ 5 Answers ]

Replacing old bathroom fixtures in a 100 yr old house. Has old 2 wire bx and I want it on its own circuit. The supply comes in from another room to the ceiling box where it goes to another room and to the wall switch then from there it goes to the medicine cabinet. I want to have this room on its...


View more questions Search