    Attic is cool but outside condenser is not working
    Our a/c unit in the attic seems to be running fine, the attic is cool (usually is hot) and the outside condenser just makes a short humming sound and the fan will not kick on.
    I have checked all circuit breakers and the thermostat. What can I do to fix this problem? Will it hurt to allow the unit to continue to cool the attic, so that cool air at least flows down to the living space? Thank you
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jul 12, 2010, 07:33 AM
    1. (Our a/c unit in the attic seems to be running fine)= is this something new? I never heard of someone cooling their attic with a/c
    2. (outside condenser just makes a short humming sound and the fan will not kick on)= is the compressor running ? Or is entire unit humming?
    3. (Will it hurt to allow the unit to continue to cool the attic, ) it's a waist of money to cool attic with a/c . Are there vents open or someway for the cool air to get into living space?
    TerryPruett's Avatar
    TerryPruett Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 12, 2010, 07:44 AM
    Comment on wmproop's post
    Yes, it just is cooler in the attic where the unit is. I was thinking maybe since the coils are up there the cool air is just not be circulated. There is nothing running outside at the condenser. There is a small amount of air coming through the ven
    TerryPruett's Avatar
    TerryPruett Posts: 3, Reputation: 1
    New Member
     
    #4

    Jul 12, 2010, 08:15 AM
    Comment on wmproop's post
    I did notice a humming noise at the outside condenser, when the unit is on up in the attic, even with the box off next to the unit outside

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC condenser fan not running nor is cool air [ 9 Answers ]

My condenser fan stopped running and there is no cool air coming from the vents. I'm wondering now though, will the cool air stop flowing just because the fan is not running, or does this mean that the compressor has gone bad? The compressor still turns on fine (it seems a bit nosier now though)...

Fan in attic not working. [ 3 Answers ]

The fan in the attic is not blowing with the a/c on (the compressor will run outside) or if I just turn the fan to on on the thermostat. However, it will run if I turn on the heater. Suggestions? Thanks!

Heat and Air not working on Attic unit, but blower working. [ 1 Answers ]

The blower is working fine on our Heating and Air Conditioning unit but neither the Air or Heat will work. The emergency Heat works fine though. The unit is a Carrier with the words American Standard written on the outside fan unit. What should I look for before calling a tech or what would this be...

AC condenser compressor and fan not working [ 1 Answers ]

The inside blower motor works, just the outside unit will not turn on. Everything is fairly new. I replaced the capacitor, contactor, and the Hard Start Kit. Everything looked fine. Niether compressor nor fan will turn on by itself. I pushed on the single pole contactor and the unit jumps to life...

Outside condenser (heatpump) not working in cooling mode [ 2 Answers ]

My Goodman heatpump consonsor will not start in cooling mode. I have 240 volt and 24 volt at the condenser, but the unit still won't turn on when I call for cooling. The unit has a defrost circuit board. Need help. Thanks


View more questions Search