    Well pump not building pressure
    With a faucet open, my pump pressure drops from 50 psi down to 30 psi, pump turns on, but no pressure builds back up. The gauge stays at 30 psi for a few minutes, then drops down to ~0 psi and the pump is making a racket. I lose water at the faucet at which point I shut down the faucet valve. Pressure now builds back up to 50 psi and the pump shuts off as it should. The top half of the holding tank appears to be empty and the bottom half is full as it should be. The weather has been very hot and dry (East coast). Do you suspect the water table or a mechanical problem?

    Thank you
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jul 11, 2010, 02:30 PM
    How deep is the well? Drilled or bored well? Is this a deep well ,shallow well, submersible or with a jet foot valve. If it is a shallow well, 25" or so, you are probably running out of water. How much water can you run out before the noise starts. If it is 10-15 gallons, you are out of water. Can you lower the foot valve?
    bthomas49's Avatar
    bthomas49 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 11, 2010, 03:06 PM
    Comment on ma0641's post
    Thanks for the comeback. The well is a deep well with the pump above ground (basement). I suspect I have a foot valve, but cannot be sure. If I do, I would not know how to lower the valve. Once I close the faucet, the pressure builds back up to 5
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #4

    Jul 11, 2010, 03:16 PM

    BT, how many pipes go from your pump down the well? If it's just one, then you can't pump from much more than 25'. If it's two, then you can get down deeper than that, and you would definitely have a foot valve. Since the pump can build pressure back to 50# once you turn the faucet off, then it would seem you have a volume problem. The pump can still build pressure, but can't supply much water.

    Try this: Run a short garden hose into a 5 gallon bucket. With the pressure at 50 and the pump not running, run water into the bucket. See how many gallons you can get before the pressure drops to 30 and the pump cuts on. At that point, turn off the faucet and time how long it takes your pump to get back to 50 and cut-off. Do a little math, and you'll know how many gallons per minute your pump is supplying. Ideally, it would be at least 5 or 6 gallons per minute. I'm going to guess that you are nowhere near that.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New shallow well pump new huge pressure tank but water pressure is terrible [ 11 Answers ]

When I had a smaller pump (shallow well) and small tank my water pressure was great. When I had to replace everything the person installing the system put a bigger pump and a huge pressure tank. It is the size of a 50 gal water heater. I replaced everything. Ever since then my water pressure is...

What is the correct suction pressure and head pressure for a 3 ton tempstar heat pump [ 1 Answers ]

When the yellow jacket brand gauges are put on a 3 ton Tempstar heat pump what should the correct suction pressure and head pressure be. I suspect it to be overcharged in freon. Because it is freezing the compressor, accumulator tank and all the lines soild ice.

High well pump pressure, but low pressure in house [ 6 Answers ]

I have a 2 year old renovated home with a well. Pressure was never really great in the house, but acceptable. The well and line to the house is about 40 years old. Inside the house is a 2 yr old Amtrol xtrol pressure tank, which feeds a 2 yr old water softening system, which feeds a whole-house...

Deep well, pressure tank/switch not building pressure [ 13 Answers ]

The only way I have water pressure is to leave the power on! I have replaced the 5 gallon pressure tank (28psi when void of water)/fittings/pressure gauge and tried 3 new 30/50 pressure switches and the problem remains the same. With the power off, the pressure drops to 0 (not 30). When I...

No pressure for 3 unit building [ 1 Answers ]

I am in a 3 unit condominium building. We are not getting any pressure from the city. We have a pump which, to the best of my knowledge, has never been used. Is it possible, somehow, that we let out all the pressue that is generally in the pipes and need to run the pump? If we run the pump what PSI...


View more questions Search