How do I wire a 4 wire cooktop to 3 wire house
Hello,
I am trying to wire a 4 wire cooktop to a 3 wire feed from the house.
Wires from Cooktop; White, Black, Bare, Red
Wires from house; White, Black, Bare
Which wires should I connect to which?
Thanks!
|
|
 |
Electrical & Lighting Expert
|
|
Jun 26, 2010, 06:41 PM
|
|
You cannot wire this cooktop to this circuit.
What you have is a 240v circuit with no neutral. You need a 120/240v circuit with a white neutral.
There is one exception to this. Can you tell us what it says on the circuit cable?
|
|
 |
New Member
|
|
Jun 26, 2010, 06:57 PM
|
|
[QUOTE=stanfortyman;2410539]You cannot wire this cooktop to this circuit.
What you have is a 240v circuit with no neutral. You need a 120/240v circuit with a white neutral.
There is one exception to this. Can you tell us what it says on the circuit cable? Yes, "E123775 8/2 WITH GROUND TYPE NM-B 600 VOLTS (UL) B. This was hooked up to a 240 cooktop. It broke and we were replacing it with a new one.
|
|
 |
Electrical & Lighting Expert
|
|
Jun 27, 2010, 04:50 AM
|
|
OK, that is "**/2" NM cable as I suspected.
You absolutely CANNOT use that cable for a 4-wire (120/240v) appliance.
That cable can be used for a 120v appliance, or a 240v appliance, ONLY.
You need to run a new circuit.
|
|
 |
New Member
|
|
Dec 16, 2011, 08:39 PM
|
|
What if I have the same issue but my circuit cable says "E30445 (UL) AWG10 CU 2CDR WITH AWG 10 GROUND TYPE UF-B 600 VOLTS SUNLIGHT RESISTANT.
|
|
 |
Uber Member
|
|
Dec 17, 2011, 05:10 AM
|
|
A #10-2 with ground cable can only be used for a 30 amp circuit either 120 or 240 volts, not for an appliance that needs both 120 and 240 volts, which requires a neutral that would be the white of a 4 wire cable.
|
|
 |
Electrical & Lighting Expert
|
|
Dec 17, 2011, 06:50 AM
|
|
 Originally Posted by smithlaw
What if I have the exact same issue but my circuit cable says "E30445 (UL) AWG10 CU 2CDR WITH AWG 10 GROUND TYPE UF-B 600 VOLTS SUNLIGHT RESISTANT.
Electrically NM and UF are the same thing. In fact, UF is a type of NM cable. So you DO have the same situation.
See replies #4 & #6.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Black wire red wire and white wire spliced to 10/3 on a 220 circuit
[ 25 Answers ]
I have installed a disconnect between my dryer receptable and a tanning bed. I want to splice the 10/3 box wire to the existing 220 wiring at the dryer.
Dryer= red, black, white and bare ground wires
10/3 wire= black, white, and bare ground
How do I splice these to allow the disconnect box to...
Wiring a 3-wire cooktop into a 4-wire box
[ 11 Answers ]
Hello,
I need to replace our GE profile glass cooktop because the glass itself shattered. I found a very similar used cooktop. However, the cooktop I'm taking out has 4 wires, black, white, red and bare copper. The one I'm putting in has 3; black, red and bare copper. Do I just match colors and...
3 wire cooktop to 4 wire supply box
[ 1 Answers ]
What is the right way to connect a Dacor electric cooktop with 3 wires (red/black/green) to a supply box with 4 wires (red/black/white/bare copper)?
View more questions
Search
|