Wiring a 3-wire cooktop into a 4-wire box
Hello,
I need to replace our GE profile glass cooktop because the glass itself shattered. I found a very similar used cooktop. However, the cooktop I'm taking out has 4 wires, black, white, red and bare copper. The one I'm putting in has 3; black, red and bare copper. Do I just match colors and go, ignoring the white? My oven is on the same circuit, wired into the same box.
Thanks,
Bill
|
|
 |
Electrical & Lighting Expert
|
|
Jan 18, 2009, 07:34 PM
|
|
 Originally Posted by billstl
Do I just match colors and go, ignoring the white?
Pretty much. Just be sure to safely cap off the white wire.
Is the new unit the same draw as the old one?
|
|
 |
New Member
|
|
Jan 19, 2009, 07:05 PM
|
|
Yes. The old unit is 220. The new cooktop itself has a plate that says 208y/120v, 60Hz, A.C. 3 wire on one line and 120/240v, 60Hz, A.C. 3-wire on the next line down.
|
|
 |
Electrical & Lighting Expert
|
|
Jan 19, 2009, 08:51 PM
|
|
That is weird. If it really were a 120/240v appliance there would definitely be a white wire at the wiring harness. :confused:
|
|
 |
Senior Member
|
|
Jan 22, 2009, 07:02 AM
|
|
 Originally Posted by stanfortyman
Pretty much. Just be sure to safely cap off the white wire.
Is the new unit the same draw as the old one?
I would not "cap off" the white wire. It should be connected to the bare copper. BONDING!!
Neutral (white) and Ground(bare copper) should be bonded.
|
|
 |
Electrical & Lighting Expert
|
|
Jan 22, 2009, 04:18 PM
|
|
 Originally Posted by Handyman2007
I would not "cap off" the white wire. It should be connected to the bare copper. BONDING!!!
Neutral (white) and Ground(bare copper) should be bonded.
WHAT?? Are you serious? NO, the neutral and ground should NOT Be connected!
If this really is a 240v "3-wire appliance you DO NOT need a neutral. You also NEVER (any more at least) connect a neutral to a ground anywhere outside the main panel.
I know what BONDING is, and this is not it!
Are you even an electrician?
|
|
 |
Senior Member
|
|
Jan 22, 2009, 04:33 PM
|
|
Hmmm, have you ever taken a look at the electrical wiring insde of an electric appliance... the neutral(white ) AND ground are Bonded within the appliance.
|
|
 |
Senior Member
|
|
Jan 22, 2009, 04:34 PM
|
|
That is on newer 4 wire appliances.
|
|
 |
Electrical & Lighting Expert
|
|
Jan 22, 2009, 04:45 PM
|
|
They are bonded, or can be bonded, because of older codes allowing it. This allowance has been removed for several code cycles now.
Like I said, a straight 240v appliance does not even use a neutral.
|
|
 |
Senior Member
|
|
Jan 22, 2009, 04:52 PM
|
|
I will neither agree nor disagree with you but I have several schematics for appliances and newer 4 wire appliances Do have a neutral that is internally connected to ground.
Good Evening...
If I could add one to this response I would...
|
|
 |
Electrical & Lighting Expert
|
|
Jan 22, 2009, 05:03 PM
|
|
 Originally Posted by Handyman2007
I will neither agree nor disagree with you but I have several schematics for appliances and newer 4 wire appliances Do have a neutral that is internally connected to ground.
Good Evening...........
If I could add one to this response I would...
This is not a grey area.
For a 120/240v appliance such as a range or dryer:
An existing circuit can be left or used as is. The code change is not retroactive.
A newer circuit MUST be a 4-wire (one being a dedicated equipment grounding conductor) with the neutral and ground separate.
A straight 240v appliance does not use a neutral.
|
|
 |
Printers & Electronics Expert
|
|
Jan 22, 2009, 05:03 PM
|
|
To begin with, electricity has nothing to do with electronics. What the manufacturer does inside his box is totally outside the electricians domain.
For electrical problems, you can use a wiring plan, but not a schematic. Schematics are on the appliance side.
Now, please stop and think this through. Power is sent to a residence by either an overhead drop or an underground lateral.
You get three wires in. Two hots and one neutral. The "Neutral" is 120 VAC away from each Hot.
The previous statement that you do not need a neutral is correct if the device that is connected only use 240VAC (a water heater). However, if the device also requires 120 VAC drop ( as in a stove or oven) then you must bring the neutral over to the device.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
3 wire cooktop to 4 wire supply box
[ 1 Answers ]
What is the right way to connect a Dacor electric cooktop with 3 wires (red/black/green) to a supply box with 4 wires (red/black/white/bare copper)?
Connecting 4 wire cooktop
[ 1 Answers ]
Can you assist me with connect a new four wire cooktop to my existing breaker panel? I have a 40 amp 2 pole breaker in my panel, but I have four wires coming from the new cooktop. I am installing a new Kenmore Elite model #44089. Do the black and red go to the breaker? The green to ground? What...
Wiring a 2 wire thermostat to a 4 wire system
[ 1 Answers ]
I have a gas furnace equipped with central air.The compressor is shot in the AC unit,and I needed to replace the thermostat so I bought a heating only thermostat.I have the blower and the w wires together on the w terminal designation and the rh on the r terminal designation, and I have the y wire...
View more questions
Search
|