    Increasing my load center capacity
    I have a weather proof CH main lug load center, grounded to earth, rated at 125 amps, with space for 4 breakers. I will be removing the 4 breakers and putting in a 100 amp breaker. From this 100 amp breaker, I will be running wires, less than a foot to a new CH 125 amp outdoor load center with 16 circuits. The old load center will function as a main breaker and the new center will function as the supply for my camp. This will be mounted on pressure treated wood and attached to the power pole at my camp.
    Am I doing this right? What size wire should I use for a 2 ft. run between load centers? I will have two hot lines coming in; a neutral and a ground. Do I hook the neutral and ground wires to the Ground Bar as in a normal installation?
    Thanks for your help. Have I missed anything?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 5, 2007, 03:53 AM
    You can use either 3- #3 copper or #2 aluminum wire for the two hot legs and one neutral, and a #8 equipment ground conductor.

    In the subpanel, the neutral needs to be connected to insulated neutral bar, and the equipment ground wire needs to be connected to an additional equipment ground bar that is bolted directly to the panel using machine screws. Use the neutral bar for white neutrals, and the equipment ground bar for bare or green ground wires.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Load Center Capacity [ 11 Answers ]

I have a new Square D load center installed rated at 100 amps. What does the 100 amp rating mean? If I replace the 100 amp main breaker with 200 amp breaker does that mean that The load center could melt if 200 amps flowed through it or that the incoming service wires could melt or what. Just...

LOAD center, scientific atlanta [ 1 Answers ]

I need a wiring diagram for a scientific atlanta load cent, series dcu-g1530or similar devise

1999 Chevy S-10 Load (Bed) Capacity. [ 4 Answers ]

Gross Rear Axle Weight is 2400 lbs but I have no clue what the axle weight is with nothing in it. Presuming less than perfect shocks/struts, do you think I'm safe to put 1200 lbs of sand in the bed to haul less than 5 miles? Thanks!

New main breaker load center - grounding [ 1 Answers ]

I currently have a fuse box that I want to upgrade to a main breaker load center. My house is in the country so I have a pole with the meter and a service disconnect. From the service disconnect it braches to my barn, well pump, and the house. (Following the main into the house) Inside on...

Load panel capacity 200 amp [ 1 Answers ]

I have a challenger load panel SB20 (20-40) CT. Which is a 200 amp panel. The number of switches currently in the panel are 19 total. Total amp of all switches is 360. Some of those circuits are dedicated to a sole source. GFCI to Whirlpool tub for example. This panel has 20 1" spots...


View more questions Search