    GFCI neutral bar/pigtail question for hot tub
    I have a 240 volt hot tub (4 wire) and it's wired in a spa pack to a GE 50 AMP GFCI breaker. An electrician did the wiring and connected both the hot tub neutral and the gfci pigtail to the neutral bar instead of to the neutral of the gfci breaker. According to everything I've read here the GFCI should trip but it doesn't and the hot tub operates fine. Is it still protected? Is it fine to leave it this way? Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 2, 2010, 03:58 AM
    The GFI circuit breaker must have the load neutral connected to the neutral terminal on the breaker, or it will not operate properly.

    Insist the electrician come back and fix it, for no charge.

    Insist that he read and follow the manufacturers instructions for the breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hot tub gfci trips [ 19 Answers ]

I'm about to pull my hair out... Gfci on hot tub trips as soon as breaker in main panel is turned on... replaced breaker with new 50 amp gfi... replaced wires from gfi box to tub... unhooked all plugs on control box... it even trips if you unhook the main hot wires to the tub... with only the...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

Hot Tub Wiring - GFCI [ 1 Answers ]

I have a hot tub currently wired at my home in the following configuration: 50amp breaker at the main panel to 50 amp GFCI breaker mounted outside, on the house near tub to Spa main panel inside tub which has a 110v GFCI module. My issue is that sometimes when I kick on the heater while the...

Extend a GFCI beaker pigtail? [ 3 Answers ]

The one outlet I have in my garage is on a 15A GFCI breaker also connected to my deck outlets. I want to run a dedicated 20A GFCI breaker to the garage outlet. I have a GE main box with a double open spot at the lower right. The GFCI breaker pigtail is not long enough to reach the neutral...

Hot Tub gfci [ 1 Answers ]

The hot tub that I'm installing requires a 240V supply but there are only three connections. The two hot leads and a ground connection, shouldn't there be a lug for the neutral wire also? The gfci breaker has a three wire with a ground (4 wires) on the line side with the white neutral on the line...


View more questions Search