    Need to upgrade circuit breaker from 20A to 30A
    I have been having a problem with my heat pump unit. I live in a new house, and it worked fine for the first two years I've lived there. Lately, the circuit breaker to the outside unit has started tripping regularly during periods of extended use (i.e. hot in summer, cold in winter).

    I've had an HVAC technician come out and test the unit, and everything is fine. He brought up that the panel on the heat pump itself lists 30A max, but the breaker installed is a 20A. He suggested I replace the 20A with a 30A.

    I have no problem doing this, as I've already replaced the 20A breaker once (thinking the breaker was the problem.) My question is:

    I have one main breaker panel, and a sub-panel. In the main panel, I have two mains (connected together) each at 200A. If I add up all the breakers in the main, I come up with 390A. One of those, of course, is a 100A to the sub-panel, which contains 80A worth of breakers. Thusly, it seems simple enough, I have 390A, if I change the 20A to a 30A I'll have 400A, and the main seems to be able to handle 400A.

    It seems a little too simple. Is this an accurate way to figure this? Can I put it the 30A in place of the 20A? I also need to check the gauge of the wire, I understand, but I'm not sure exactly what it should be. There seem to be a lot of different opinions, which is odd, but my guess (or average of those) would be for a 30A, I need #10... for a 20A, #12. Is this correct? I'm hoping that (as the evidence suggests) the house builders put it the right wire but the wrong breaker.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 5, 2006, 08:33 AM
    HVAC units fall under Article 440 of the National Electric Code, and this is one situation that a larger breaker is allowed on a smaller wire.

    The heat pump, or any HVAC refrieration unit, should have on the nameplate a MCA, or Minimum Circuit Amps, which sizes the wire, and it will also list the Maximum OCPD, or circuit breaker/fuse.

    The MCA is probably for #12, and the OCPD is 30 amp, as the HVAC tech stated, and this confuses many electricians. Once they see #12 wire, they automatically install a 20 amp breaker, and pay no attention to the nameplate.

    You unit states it needs a 30 amp breaker, just to be sure #12 is fine, does the nameplate have the MCA listed? I just want to check before I tell you to install a 30 amp breaker on #12 wire, which mostly be the case, and be allowed.

    Adding up the rating of each breaker is in a panel is irrelevant. Nothing is sized or needs to match this sum.
    WilWa's Avatar
    WilWa Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 5, 2006, 12:04 PM
    The nameplate lists:

    Minimum Circuit Amps 18.7
    Max Fuse 30 A
    Max Ckt-Bkr(*) 30 A
    *HACR Type Recommended

    (My wife also just told me (she talked to the HVAC guy) that he said the wiring, etc. doesn't need changed... just the breaker.)

    (Please let me know if you concur. Thanks for your help! =))
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 5, 2006, 04:36 PM
    I concur, the wirng can remain #12 and you can use a 30 amp breaker, and this will conform to code.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuit breaker [ 3 Answers ]

A circuit breaker connected to the kitchen tripped twice. I had an electrician in but the problem persists - in fact, the very day the electrician came. It does not seem to be caused by any one particular appliance. The first time I was using the waste disposal and the next two times nothing was...

Circuit breaker blowing [ 5 Answers ]

When I run my dryer, I blow a circuit after about 5-10 minutes. Any suggestions?

GFCI Circuit Breaker. [ 2 Answers ]

I recently ran a branch circuit to the exterior of the house to add a receptacle on the patio. The existing 15 amp breaker protected a circuit that had only three plug outlets and one switched ceiling light. The circuit is very lightly used. So I want to add GFIC protection in the form of a breaker...

Circuit breaker load [ 2 Answers ]

I'm remodeling my basement, & putting in a lot of elec'l outlets. Wondering how many outlets, or how do I figure how many, I can put on one ckt brkr. I'm using no. 14 Romex & 15 amp brkr. Tom :confused:

Circuit breaker popping [ 4 Answers ]

We just got a new refrigerator and the circuit braker for the air conditioning keeps popping. We live in Central FL by Daytona and it is really hot right now but we can't keep the air running. Help!!


View more questions Search