    What type #6-3 alum. Wire from my main service across the basement to aluminum URD
    The URD is in 2" metal conduit. It services a 50 amp detached garage.What type aluminum wire should be used between the main panel, and the junction box located at the "service" side of the conduit in the basement? Can I run aluminum through the basement in "free air"?




    --------------------------------------------------------------------------------
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 15, 2010, 06:46 AM
    SER cable is typical for an aluminum feeder cable, allowed to be installed outdoors or inside, supported every 4.5 feet.

    URD or any other cable similar is not allowed to run free air in a building.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What type #6-3 alum. Wire from my main service across the basement to aluminum URD [ 0 Answers ]

The URD is in 2" metal conduit. It services a 50 amp detached garage.What type aluminum wire should be used between the main panel, and the junction box located at the "service" side of the conduit in the basement? Can I run aluminum through the basement in "free air"?

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

Redistribution of existing 3 wire aluminum #4 50 amp line from main panel [ 1 Answers ]

How do I connect an existing 3 wire aluminum #4 line from my main panel to a sub panel that I will use to supply a 40 amp electric oven and a 20 amp circuit for a microwave. Do I connect the bare wire to the ground bar or common and do I a connect the nutral bar to the ground bar. I know how I...

Wire type from main panel to adjacent subpanel [ 1 Answers ]

I have a 200 amp main panel that is nearly full and I plan on adding a 100 amp subpanel close by in the basement of my residence (south-east PA). I happen to have some wire available that I believe is adequate gauge (based on reading many other posts) but I want to make sure the specific wire I...

Connecting large gauge aluminum wire to service panel [ 2 Answers ]

I've completed a beautifully (inspector approved) installation of a new 200 amp service panel to my home (upgraded from 100 amp). I have now strung a 0/0 underground aluminum cable in sched. 80 conduit from my barn to the main panel to connect a sub-panel in my barn to this new 200 amp panel. ...


View more questions Search