    I have a split Heat/AC. AC appears to be external to the home and is on its own CB.

    Heat is installed in the attic.

    This afternoon, my son discovered that the blower motor in the attic was still running even though the heat was turned off at the thermostat.

    The thermostat is a six wire, Select Comfort model. My son, removed the batteries from the thermostat fan motor still ran. Then he removed the slow-blow fuse for the thermostat and the blower still kept running.

    Finally, he went to the main panel and shut the A/C breaker down. Blower motor still ran. Then killed the Heat breaker which finally shut the motor down. When he reset the breaker, the motor did not restart.

    Since the motor did not shut down until the power was cut, is telling me that the failure may be in a controller board within the heat plant.

    Please, I am open to any and almost all reasonable solutions.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 14, 2010, 02:13 PM

    Is this a gas furnace or a electric furnace?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Apr 14, 2010, 02:20 PM

    Josh,

    It is an electric furnace, mounted in the attic.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Apr 14, 2010, 03:11 PM

    Sounds like you may need a new heat sequencer.

    http://www.drillspot.com/pimages/408/40804_300.jpg
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Apr 15, 2010, 07:27 PM

    Josh,

    I am a reasonably skilled tech with a very strong background in electromechanical devices.

    Assuming I can get to the attic device (I understand that there are two of them up there) where would I start looking for the heat sequencer?

    How big of Chinese Fire Drill is it to swap one out?

    Obviously, I will need the correct model number to get the correct heat sequencer, but do you favor one model line over another?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #6

    Apr 15, 2010, 08:26 PM
    Donf, there will be a removable panel which houses all the electrical components. On the door of the furnace there very may well be a schematic. If you post the MFG and the model number, one of us will be able to help you more thoroughly. A heat sequencer is basically a relay or contactor. If the fan continues to run after the control circuit is broken, it's probably sticking. No attempts should be made by you to repair this until you turn off all the power. Next time it happens, try cycling the fan switch on the thermostat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower motor won't stop running [ 6 Answers ]

Hello to every one, maybe someone can help with my problem. My furnace blower motor will not stop running. When the t-stat calls for heat it blows warm air after the heat cycle the blower blows cool air,so it's kind of working against its self. The only way the blower will shut off is if you turn...

Blower motor not running [ 1 Answers ]

Okay, so the heating/ac guy cannot get out for a few days, so I started diagnosing things myself. My blower (rheem residential gas/ac unit, less than 6 years old) was slowing down and finally quit. I had the motor checked out and it was dead at this point (very dirty, had been running on very...

Goodman furnace will ?heat motor? And blower motor will run but not at same time [ 2 Answers ]

I have a 2 year old Goodman, gas, no heat pump. There is a flashing LED that blinks once ever 4 seconds. Also, blower motor does not stay on always. We did smell something like an electrical burn. I'm guess my blower motor is fried?

Blower motor not running [ 7 Answers ]

Hi, I have a rheem furnace in which the blower motor buzzes but does not run. I replaced the motor, and the capacitor(15/370 MFD) but the same problem persists. The motor that was initially on the system (51-18716-01) is no longer sold so I bought the one that replaces it ( 51-23017-42). The...

Blower motor running constantly [ 6 Answers ]

We have an older bryant furnace It heats up but the fan runs on and on there is a switch that says summer fan when its on it runs constant if you switch that off the fan won't blow at all help needed soon thanks Michelle


View more questions Search