    Blower motor not running
    Hi,

    I have a rheem furnace in which the blower motor buzzes but does not run. I replaced the motor, and the capacitor(15/370 MFD) but the same problem persists. The motor that was initially on the system (51-18716-01) is no longer sold so I bought the one that replaces it ( 51-23017-42). The only difference between the two is that this new motor has two brown capacitor wires. When I attach both brown capacitor wires to the capacitor, the motor runs but it runs slow and it hums and after a minute turns off. If I attach only one of the brown capacitor wires coming from the motor to the capacitor the motor buzzes but does not run. If I then turn the blower with my hand, the blower runs fast at its normal speed.
    Do the brown wires from the motor provide electricity from the motor to the capacitor, or from the capacitor to the motor? I checked the voltage on both wires when not attached to the capacitor, and one the voltage coming from one is about 158V and the other around 4V. I see the same voltage on the old capacitor.I see a Voltage of 4V on the white wire from the motor attached to the capacitor, and around 4V on the beige wire coming from the junction box that is attached to the capacitor.
    What do you guys think is the problem?
    Thank you very much in advance for your input.

    Merry Christmas, and happy holidays.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 23, 2007, 05:05 PM
    Did you buy a new Capacitor for the motor you are now using?
    Could very well be a bad Capacitor.
    alsk123's Avatar
    alsk123 Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 23, 2007, 08:09 PM
    Hi,

    Thank you for the replies. I did buy a new capacitor, and a motor.
    Here are the wires from the motor and how I have connected them:
    Black,red, white, blue, yellow, brown, brown
    What I have done is to connect the black from the motor to the black coming from the jbox, and the red from the motor to the red coming from the jbox. I also have the while from the motor connected to one side of the capacitor. On the same side of the capacitor, I have also connected the white coming from the jbox. On the other side of the capacitor I have connected the two brown wires, but as I have mentioned when I do that the motor hums and runs very slowly for about 30 seconds before shutting down. If I connect only one of their of the brown wires to the motor buzzes, and then if I turn the blower with my hand, it runs normal. The yellow and blue I have not connected to anything since it was also the same on the old motor.

    Thanks again for your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 23, 2007, 10:00 PM
    Without seeing the motor wiring diagram I am going to take a educated guess. I believe both brown wires go to the capacitor. One to each side of it.

    The white goes to the common or neutral side or the motor power circuit and then the black,red.blue and yellow are the different speeds. I assume this is a 120 volt motor?

    Give this a try. There is also some motor wiring help in the sticky notes at the beginning of this board.
    alsk123's Avatar
    alsk123 Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 24, 2007, 06:02 PM
    Thank you very much for your help. The wiring you suggested works. I am surprised that it is not the same as the sticky on the motor.
    Happy Holidays.
    AC Doc's Avatar
    AC Doc Posts: 12, Reputation: 1
    New Member
     
    #6

    Dec 24, 2007, 07:01 PM
    The key factors for replacing a motor are HP= Horsepower, RPM=Revolutions per minute, and voltage. The high voltage wires should be one to the incoming voltage and the other to a relay or sequencer (SWITCH). This switch could be bad and not passing a good connection. You can check it by jumping around it. The two brown wires get connected to the new capacitor only. You may have a two speed motor that gets high speed for heating and medium for cooling. Make sure the new capacitor is what the motor requires. It should be written on the label.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 24, 2007, 08:33 PM
    Quote Originally Posted by alsk123
    Thank you very much for your help. The wiring you suggested works. I am surprised that it is not the same as the sticky on the motor.
    Happy Holidays.

    Sometimes the diagram on the motor can be confusing. Glad you got it going. Merry Christmas
    limuobai's Avatar
    limuobai Posts: 1, Reputation: 1
    New Member
     
    #8

    Mar 21, 2008, 08:32 PM
    Quote Originally Posted by alsk123
    Hi,

    I have a rheem furnace in which the blower motor buzzes but does not run. I replaced the motor, and the capacitor(15/370 MFD) but the same problem persists. The motor that was initially on the system (51-18716-01) is no longer sold so I bought the one that replaces it ( 51-23017-42). The only difference between the two is that this new motor has two brown capacitor wires. When I attach both brown capacitor wires to the capacitor, the motor runs but it runs slow and it hums and after a minute turns off. If I attach only one of the brown capacitor wires coming from the motor to the capacitor the motor buzzes but does not run. If I then turn the blower with my hand, the blower runs fast at its normal speed.
    Do the brown wires from the motor provide electricity from the motor to the capacitor, or from the capacitor to the motor? I checked the voltage on both wires when not attached to the capacitor, and one the voltage coming from one is about 158V and the other around 4V. I see the same voltage on the old capacitor.I see a Voltage of 4V on the white wire from the motor attached to the capacitor, and around 4V on the beige wire coming from the junction box that is attached to the capacitor.
    What do you guys think is the problem?
    Thank you very much in advance for your input.

    Merry Christmas, and happy holidays.
    I have exactly the problem as you had. I don't understand HVAC1000's answer. Did you have to put 2 brown wires one on each terminal of the capacitor? I did that and tripped circuit breaker. Could you describe you wiring again?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace blower motor start and keeps running won't stop [ 12 Answers ]

I have a Carrier central furnace (furnace model 58GP050-BA). Now with the thermostat off the fan set to auto and the Gas pilot is on. When turn on the power switch to the furnace, the blower motor start and keeps running and won't stop. I have to turn off the power switch to the furnace to turn the...

Blower motor won't stop running [ 6 Answers ]

Hello to every one, maybe someone can help with my problem. My furnace blower motor will not stop running. When the t-stat calls for heat it blows warm air after the heat cycle the blower blows cool air,so it's kind of working against its self. The only way the blower will shut off is if you turn...

Saniplus motor running on [ 3 Answers ]

I really hope someone can help us. We purchased our house in August 2004 and there was an ensuite shower room using a saniflo system already installed. The unit worked perfectly for 17 months (Dec 06) until the motor burned out, we assumed through age as we had no idea when the system had first...

Furnace's draft motor keep running [ 5 Answers ]

Hi, My furnace recently starts acting weird. After running up to satisfied temperature, the thermostat stops normally, then the blower stops 30 seconds later as usual, but the draft motor sometimes keep on running forever. Turn off then on the power to furnace obviously reset it to normal,...

Blower motor [ 1 Answers ]

Blower motor doesn't come on, turn up tstat and furnace lights?