    Using Double pole circuit breaker for two separate circuits
    I am wiring my basement with 3 circuits for about 24 receptacles. We used to have electric baseboard heat and the 20 Amp Double pole breakers from the heaters are still there but disconnected. Can I use each double pole breaker for two separate circuits? Can I use one leg of another double pole breaker for a circuit? Am I being dangerous as well as a cheapskate?
    crigby's Avatar
    crigby Posts: 4,343, Reputation: 107
    Outdoor Power Equipment Expert
     
    #2

    Jun 30, 2009, 11:22 AM

    Hi,
    Yes you can use both sides of the unused breaker each for different circuits, and the 20 Amp rating calls for 12 AWG wire to be correct.
    I am unsure about the other; do you mean to say it is unused? If so then I would say yes. If not I would consider another alternative. One might be to change a single breaker to a double, if you have no room to add another breaker.
    The important consideration is that the totals for all circuits used do not exceed the rated amperage of your box/service.
    Peace,
    Clarke
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jun 30, 2009, 11:37 AM

    A typical single pole circuit breaker, new, only costs about $4-$6 each.

    If you need three, that would be the most $18.00.

    Splurge and buy new circuit breakers.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

30 Amp Double Pole Breaker is hot and tripping [ 10 Answers ]

Hi, I just got a Maytag Neptune Dryer a week ago. I have it plugged in to our old dryer outlet (which was replaced less than a year ago) which is 3 prong. The dryer voltage is 240 volts and I am running it on a 30 amp double pole breaker. The problem is, this is new electrical wiring and a...

Using a Double Pole Breaker to feed two circuits [ 11 Answers ]

I have 40' run from the main panel with BX and want to use 14/3 instead of two runs of 14/2. Is there a problem using a double pole breaker (15amp) to feed (with 14/3) a split receptacle and then a lighting circuit on one half and 4 receptacles on the other? Is the only drawback is when one...

How Double Pole Circuit Breaker Trip? [ 9 Answers ]

On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search