    Running refrig. Pipe over 50 ft.
    If I increase my suction from 3/4 to 7/8, do I need to increase my liquid line to? Going 70 ft. to attic. Thanks
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 13, 2010, 02:25 PM

    What ton unit? And how many ft of vertical run?
    johnair77's Avatar
    johnair77 Posts: 59, Reputation: 1
    Junior Member
     
    #3

    Apr 13, 2010, 03:05 PM

    2.5 ton, 50 ft. vertical
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Apr 13, 2010, 03:47 PM

    This may also require a crankcase heater and a hard start kit.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    Apr 13, 2010, 04:30 PM

    I would say 7/8 - 3/8 should do this OK with a 2.5 unit.
    johnair77's Avatar
    johnair77 Posts: 59, Reputation: 1
    Junior Member
     
    #6

    Apr 13, 2010, 06:50 PM

    Thanks for the input, some people even go so far as putting a suction accumulator or liq. Solenoid.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    Apr 13, 2010, 08:17 PM

    A suction accumulator would also be a very good idea.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Apr 14, 2010, 05:12 AM
    For a super deluxe job a receiver (if the condenser is not large enough to take all the liquid) and a pump down solenoid will control the weight of the column of liquid refrigerant upon shut down. This will prevent compressor oil wash out from the bearings etc.

    Quick Facts: Migration And Pump Down Systems - Service and Maintenance - Extra Edition - Air Conditioning, Heating & Refrigeration NEWS

    While possibly not critical there will also be a loss of cooling capacity due to the 50 foot height.

    Meier Supply - Pump Down

    Liquid slug or liquid in the crankcase will kill a compressor quickly so doing the job correctly will have many benefits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pipe Creak in Ceiling when Running Dishwasher? [ 2 Answers ]

During my dishwasher drain cycle or when I drain water from my kitchen sink, I can hear a pipe in the ceiling(directly above the dishwasher) make a “creaking” sound – similar to the sound wood makes when it expands and contracts. It also sounds like a drip, but the sound is so pronounced that I...

Running water sound from pipe [ 2 Answers ]

Hello, As soon as I turn the thermostat on, running water sounds coming out from pipe would last for about half a hour or so and then it disappears. It will recur after a while. It is extremely annoying at the middle of quiet night that wake everybody up. I am using Weil-McLain water Baseboard...

Slow running water pipe [ 10 Answers ]

I have a half bathroom and the hot water faucet just dribbles out. I have run the water with just the hose connection and replaced the valve but it is still dribbling out. I suspect it is either clogged in the copper pipe or there is build up blocking it from having a water softner. Is there some...

Water running from outlet pipe. [ 3 Answers ]

I have water continuously running from an outlet pipe on the side of my house (not the AC condensation pipe). The water is warm and it appears that my hot water heater is emptying and filling continuously. No other appliances are running and there are no signs of leaks anywhere in or around the...


View more questions Search