  • Apr 13, 2010, 01:59 PM
    johnair77
    Running refrig. Pipe over 50 ft.
    If I increase my suction from 3/4 to 7/8, do I need to increase my liquid line to? Going 70 ft. to attic. Thanks
  • Apr 13, 2010, 02:25 PM
    Joshdta

    What ton unit? And how many ft of vertical run?
  • Apr 13, 2010, 03:05 PM
    johnair77

    2.5 ton, 50 ft. vertical
  • Apr 13, 2010, 03:47 PM
    KISS

    This may also require a crankcase heater and a hard start kit.
  • Apr 13, 2010, 04:30 PM
    Joshdta

    I would say 7/8 - 3/8 should do this OK with a 2.5 unit.
  • Apr 13, 2010, 06:50 PM
    johnair77

    Thanks for the input, some people even go so far as putting a suction accumulator or liq. Solenoid.
  • Apr 13, 2010, 08:17 PM
    Joshdta

    A suction accumulator would also be a very good idea.
  • Apr 14, 2010, 05:12 AM
    hvac1000
    For a super deluxe job a receiver (if the condenser is not large enough to take all the liquid) and a pump down solenoid will control the weight of the column of liquid refrigerant upon shut down. This will prevent compressor oil wash out from the bearings etc.

    Quick Facts: Migration And Pump Down Systems - Service and Maintenance - Extra Edition - Air Conditioning, Heating & Refrigeration NEWS

    While possibly not critical there will also be a loss of cooling capacity due to the 50 foot height.

    Meier Supply - Pump Down

    Liquid slug or liquid in the crankcase will kill a compressor quickly so doing the job correctly will have many benefits.