Goodman furnace
Compressor kicks on blower kicks on but blower will go off and on ervery few minutes and lets the charge line freeze up and thaw.
|
|
 |
Heating & Air Conditioning Expert
|
|
Apr 6, 2010, 05:17 AM
|
|
You need to find out why the blower is cycling on and off. It might be going out on the overload from a motor overheat condition caused a dirty air filter,closed registers, or restricted return air grill can cause this. Also a defective blower motor run capacitor can also cause this type of problem. Last but not least is the possibility that the blower motor itself is defective but the other items should be checked first. You will need some skill and tools/meter to make a final determination.
One quick check is to put the thermostat blower switch to ON instead of automatic. This should cause the blower to run all the time. If not it is probably one of the items mentioned above.
|
|
 |
New Member
|
|
Apr 6, 2010, 11:07 AM
|
|
 Originally Posted by hvac1000
You need to find out why the blower is cycling on and off. It might be going out on the overload from a motor overheat condition caused a dirty air filter,closed registers, or restricted return air grill can cause this. Also a defective blower motor run capacitor can also cause this type of problem. Last but not least is the possibility that the blower motor itself is defective but the other items should be checked first. You will need some skill and tools/meter to make a final determination.
One quick check is to put the thermostat blower switch to ON instead of automatic. This should cause the blower to run all the time. If not it is probably one of the items mentioned above.
The blower works fine during the heating season, it doesn't start going on and off until you turn on the A/C. I don't think its on long enough to get hot.
|
|
 |
Heating & Air Conditioning Expert
|
|
Apr 6, 2010, 11:38 AM
|
|
Usually the blower motor uses a different speed for A/C than it does for heat. So in actuality one set of winding in the motor is being used for heat but another set OR series of windings is being tapped for A/C which is a higher speed. If the outside unit is not shutting off with the blower motor than the items I mentioned should still be checked out. This is one of those items where a amprobe meter is very helpful. If you have one of those you can monitor the current draw of the motor and compare it to the listed draw on the motor itself or the furnace label. Ususlly there is no instant cure for this type of problem it needs to be tracked down and the offending part replaced. Otherwise it could be a costly repair if guess work is used.
|
|
 |
New Member
|
|
Apr 6, 2010, 12:00 PM
|
|
 Originally Posted by hvac1000
Usually the blower motor uses a different speed for A/C than it does for heat. So in actuality one set of winding in the motor is being used for heat but another set OR series of windings is being tapped for A/C which is a higher speed. If the outside unit is not shutting off with the blower motor than the items I mentioned should still be checked out. This is one of those items where a amprobe meter is very helpful. If you have one of those you can monitor the current draw of the motor and compare it to the listed draw on the motor itself or the furnace label. Ususlly there is no instant cure for this type of problem it needs to be tracked down and the offending part replaced. Otherwise it could be a costly repair if guess work is used.
Thank you for your help, it is a very nice thing you are doing.
|
|
 |
Heating & Air Conditioning Expert
|
|
Apr 6, 2010, 12:35 PM
|
|
Your welcome.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Goodman Furnace
[ 1 Answers ]
My furnace is pulsating, gas valve is clicking on and off rappidaly, I shut it off for a short time then it will work for a few hours then start acting up again installed new air pressure switch no change,do you think I should replace the flame sensor.
Goodman furnace
[ 1 Answers ]
I have a goodman furnace about 8 years old model number is gmp100-3. the problem i'am having is it wants to keep running and starts up while blower is going in the winter during running tries to ignite while still running.could you give me some idea what this problem could be.thank you:confused:
Goodman furnace
[ 1 Answers ]
I would like more info about Goodman furnaces.
I just had a man look at my old furnace and give me a bid of $1,450.00 to take out the old one and install a Goodman 80% and bring the old piping up to code.
Thanks... jorjee
View more questions
Search
|