    200 amp service cable can this be 18ins
    I have a cable running through my garden which is 18ins" below the surface it supplies 93 houses should it be deeper and should it be running through the middle of my garden can any one answer my question in terms that I can understand? Many thanks Ali
    manhattan42's Avatar
    manhattan42 Posts: 143, Reputation: 11
    Junior Member
     
    #2

    Mar 27, 2010, 08:36 AM


    You don't specifiy what 'kind' of cable this is: Electric? Cable TV? Telephone?

    If it is electrical cable and the cable is in conduit, it is permitted to be run at an 18" minimum depth.

    Otherwise, if it is not in conduit, it is required to be at least 24" deep.

    Some electric utilities require service conductors to be at least 30" or more deep regardless of what electric codes say.

    Should it be under your garden?

    Yes, probably.

    It is there by legal easement granted to your associated community or the municipality or the electric company or all 3.. And should not be disturbed under any circumstance.

    You are required by law to call state agencies before you dig anywhere on your property.

    Call 811 is the new national number for call-before-you-dig. It will put you in touch with your state's call-before-you dig agency.

    http://www.call811.com/

    Look here for state specific information:

    http://www.call811.com/state-specific.aspx

    If you dig and damage any utility lines without first calling and getting permission to dig, and having each utility come and mark on your property precisely where the buried utilities are located, YOU will be held legally liable for any damage you cause to the utility lines: sewer, water, telephone, cable TV, electric, etc... even if these lines are located within the bounds of your own private property.

    You will be required to pay for any damaged utilities and will be additionally be fined.

    In my state the fines start at $1500 per offense and quickly go up from there.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 27, 2010, 10:56 AM

    If it is a utility line then it is most likely required to be deeper than 18" through private property.
    In fact, if this is a distribution line actually feeding 93 homes then it should NOT be running through the middle of private property.
    If it is near the property line then it is most likely in a right-of-way that is not actually your property. Most roads are much wider than the actual pavement itself. They extend into the grass/property several feet.

    Ali, can you give us some more detail that just "a cable running through my garden"?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Mar 28, 2010, 04:41 AM
    I do not think this poster is from North America, and if so, all bets are off. Codes are not the same as US or Canada in other countries.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

200 amp service 4/0 ser cable in 2" conduit? [ 1 Answers ]

What should I run from my disconnect switch to my panel box inside for my 200 amp service. I have 2" PVC ran from the disconnect to the panel. I thought about using 4/0 SER but then read somewhere that you are not suppose to put it in conduit because of possible temp problems? Is this correct or...

What is the cable/wire gauge (product name) for installing 200 Amp Service Entrance [ 1 Answers ]

I am installing a new service entrance to upgrade my home electrical service to 200 amps. 1 Please tell me what gage wire is required from the meter to the weather-head? The service panel with main breaker is inside the laundry room 25 feet from the outdoor meter loop. I will run the...

200 amp service cable [ 1 Answers ]

Good moring everyone! Quick question, I'm still in the process of upgrading to 200 amp service. I've purchaced a panel box and the guy I bought it off said he'll give me the service cable with it. The question I'm trying to find out is, the size wire he is giving me going to work 2/0, 4/0, 6/0...


View more questions Search