    USE Aluminum Underground Wire
    I need to run power underground from my house to my dock to operate my boat lift. What I was wanting to do was put a 40amp sub panel at the beginning of my dock. I have 400 amp service at the house. It's a 600 feet run fom the house to the dock. Then a 200 feet run from the sub panel to the 20 amp plug. There are 2- 3/4hp 115v motors on the boat lift. I would also like to run a second plug for my boat's battery charger on the same circuit. Lift and charger will not be running at the same time. I was thinking about running 2-2-2-4 urd cable from house to sub panel and 10-2 from sub panel to plugs. Will that work? If not please give suggestions.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Mar 22, 2010, 02:50 PM

    Not doing any voltage drops calcs which will be significant, I have a few questions and comments.

    Questions:
    1. What is the power requirements for the lift? i.e. Breaker size
    2. Will both motors operate at the same time

    Comments

    1. GFCI protection, I believe, is required.
    2. Conduit for the doc.
    3. THWN, single wires for wet locations are required even if in conduit. Usually THHN may be dual mark THWN, but there are cases that it isn't.
    4. 1000' and 2 motor loads are significant.
    OTT540's Avatar
    OTT540 Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 22, 2010, 03:23 PM

    20amp breaker is required.
    I can run each motor together or one at a time they each have there own controls.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Mar 22, 2010, 04:00 PM

    For the 200' length, I'd go with #4 copper THWN for a 2.1% drop at 20 A non-continuous at 200'.

    For the 600' length, I'd go with 4/0 or 0000 Aluminum for a 2% drop.

    Getting below 3% total would be better.

    350 kcmil Aluminum wire would give you a 1.3% drop for that segment. Total drop would be below 3%.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Mar 22, 2010, 04:56 PM
    For the 600 foot run, the #2 will work fine, allowing the max of 5% V voltage drop, and assuming one motor on each 120 volt leg of the 4 wire 120/240 volt #2 Al URD feeder.

    The 200 foot run will need #8 to run only one motor using a 2 wire cable. If you need both, then use a 3 wire cable, again to have both 120 legs, one for each motor.

    Go here:

    Southwire - Delivers Power

    And enter aluminum wire, direct bury, 600 feet, 5% Vd, 120 volts, and 15 amp load for the #2, direct bury, copper wire, 200 feet, 5% Vd, 120 volts, and 15 amp load for the #8 wire.

    The charger load is insignificant.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Aluminum Wire [ 2 Answers ]

My sister bought a house and then discovered she has aluminum wiring. After promising to help her out, I quickly realized I was in over my head. First of all, I am a Master Electrician, but I haven't done residential wiring in years, other than personal home improvements. I work mostly...

Runnig wire underground [ 3 Answers ]

I'm am getting ready to run electric wire from my house to my garage, which is approx. 140 feet and 80 feet of that is underground. I don't know what size wire or what kind to use for underground. I want to have a 200 amp service, and single phase 220volts. Any help on this would be greatly...

How to safely wire aluminum to copper wire [ 5 Answers ]

I am switching a non-programmable t-stat to a Honeywell 5-2day programmable one that is for baseboard, covectors and fan-forced heaters. The model number is RLV430A. I have a wall Cadet heater so it should be OK. Problem is when I opened the package the wiring on the t-stat is aluminum. ...

Copper or Aluminum wire [ 2 Answers ]

Hi I just replaced my Suncutter Package system with a Goodman Package system. The question is should I replace the (main power supply to AC disconnect) aluminum wire with copper? Thanks Brian

Broken underground wire [ 3 Answers ]

Could a broken underground wire cause enough heat to melt the snow At that spot and not kick out the circuit breaker?


View more questions Search