    Wiring a 50 amp sub panel
    I am wiring a 50 amp sub panel in my shop. It comes from a 100 amp sub panel in the garage. I went to the store and got what I thought was #6 3wire with ground. What I got was 6/3 w 10g ground. This new sub is 58 feet from that panel, I measured it exactly.

    Do I need to sink a ground rod at the shop and if so how far from the new sub can it be?
    If so can I use this cable and just not use the ground? The stamp on the cable says " AWG 6 CU 3 CDR with AWG 10 ground type NM-b 600 volts"

    Or do I need to get 6/3 with 6g ground and ground it back the garage sub panel.
    Most of the cable run through the garage walls and aprox 7' under a deck in conduit, then the new panel will be just inside the shop wall at the spot were it inters w/ a 1' turn, up.
    The shop and Garage are separated only by the deck.
    I think I gave all the needed info for a proper answer.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Feb 26, 2010, 05:20 PM

    The #10 ground in the 6/3NM is fine. That is correctly sized.

    The panel at the shop does need a ground rod since it is in a detached structure. You MUST also use the ground wire in the cable. The ground wire in the cable and a ground rod are two completely different things serving two very different purposes.

    One problem I see is that you CANNOT run the NM cable in conduit in a wet location. Even though this conduit is not below grade (an automatic wet location) it is in direct weather and would be considered a wet location, even inside the conduit.

    Be sure to not bond the neutral bar in the sub and keep the grounds and neutrals separate. You will probably need an add-on ground bar.
    DragonWire's Avatar
    DragonWire Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 26, 2010, 07:27 PM
    That was fast thank you. But now I'm even more confused. I guess I need to talk to a local electrician and get the exact instructions. And looks like I can't use the cable I got.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring my 125 amp sub panel [ 0 Answers ]

Hello all, I'm new to this so excuse me if I am redundant but I couldn't find this questions anywhere else. I have a 125 amp sub panel in my garage. It was previously wired before I purchased the house. The old service in the house was 100amp - since then it's been upgraded to a 200 amp service....

100 amp sub-panel wiring [ 1 Answers ]

When wiring a 100 amp sub panel do you have to run a neutral and a ground wire?

100 Amp Sub Panel Wiring [ 2 Answers ]

I know that question has been asked a hundred times so forgive me. I just wanted to make sure with my layout and for code that I was doing it right. If it makes a difference for the code requirements I line in NJ. I am running a 100 amp sub panel from my basement to my garage. I would prefer to...

Wiring 125 Amp Sub Panel [ 1 Answers ]

I have a cutler Hammer 125 amp main lug panel that I have installed for a sub panel to feed an out door kitchen and a sun room. The sub panel has 2 lugs for connecting hot wires and 1 lug for connecting a neutral. The sub panel will feed 4 ceiling fans, 9 lights, 1 bath heater, 1 refrigerator and...

Sub panel 40 amp wiring [ 1 Answers ]

I have a 70 amp sub panel. I'm trying to figure out how to wire in a 40amp breaker in the sub from the panel in my house. I have two hot wires coming in to separate lugs, one neutral, but the breaker itself has one trip/reset lever yet has two screws on the bottom of the breaker;one on each side....


View more questions Search