    Wiring a three wire light to existing four wires
    Just bought a foreclosed home where a lot of the lights were taken by the previous owner. I am trying to put a light over my kitchen table. I bought a light w/ the usual two wires plus ground, but the existing wiring from the previous/removed light has a black, white, ground, red and another single black coming out. There is only one switch on the wall for this light, and it is a dimmer. How do I wire this light to dim?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Feb 25, 2010, 05:20 PM

    Switch Location may have a red and black and only 1 being used, I would use a meter or a bulb in a socket and see what does what with dimmer.
    If you have no tester or indicator, connect white to white, then black to each of the others 1 by 1 and 1 should work with the dimmer, 1 may always be hot. Do not work on live lines unless you understand the shock hazzard and how to deal with it.
    You may find an extra wire at the switch box not hooked up and capped off.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Feb 25, 2010, 05:26 PM

    Look again, there should be two white wires. A wire is a wire, a cable is two or more wires in an outer covering. Sounds like you have a 3-wire cable and a 2-wire cable in the ceiling box.
    Remove switch and tell us the number and what kind of cables you have there. Also tell us what wires are connected to the switch.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Feb 25, 2010, 05:29 PM

    Hk, the extra black is odd, should also be an extra ground? Besides the white, if cable?
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #5

    Feb 25, 2010, 05:40 PM
    So I guess I was a little vague. Coming from the ceiling box there are four wire nuts and the ground. Wire nut #1 has three white wires, #2 has two red wires, #3 has two black wires and #4 has one black wire. The switch is a lutron dimmer with two black wires coming out of it, and a green ground attached to it. One of the blacks goes to another black and then up into some romex, and the other black goes into a butt connector with the black from the switch next to this one(which is for the recessed lights also on a dimmer), another black, and two reds.
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #6

    Feb 25, 2010, 05:40 PM
    So I guess I was a little vague. Coming from the ceiling box there are four wire nuts and the ground. Wire nut #1 has three white wires, #2 has two red wires, #3 has two black wires and #4 has one black wire. The switch is a lutron dimmer with two black wires coming out of it, and a green ground attached to it. One of the blacks goes to another black and then up into some romex, and the other black goes into a butt connector with the black from the switch next to this one(which is for the recessed lights also on a dimmer), another black, and two reds.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    Feb 25, 2010, 05:41 PM

    Agree Strat. I'm betting that OP is seeing two whites connected with wire nut and thinking it is one wire.
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #8

    Feb 25, 2010, 05:47 PM
    Quote Originally Posted by hkstroud View Post
    Agree Strat. I'm betting that OP is seeing two whites connected with wire nut and thinking it is one wire.
    My apologies, new here and trying to figure out how to respond to you guys
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    Feb 25, 2010, 06:02 PM
    So you have two 3-wire cables and a 2-wire cable in the ceiling box. You have a 2 gang switch box with a switch for this light and a switch for the recessed lights. I confused about how many cables are in the switch box.
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #10

    Feb 25, 2010, 06:11 PM
    Quote Originally Posted by hkstroud View Post
    So you have two 3-wire cables and a 2-wire cable in the ceiling box. You have a 2 gang switch box with a switch for the recessed lights. I confused about how many cables are in the switch box.
    There are four romex cables coming into the switchbox on the wall. Two of them are red, white, black and ground, and the other two are black, white and ground.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #11

    Feb 25, 2010, 06:23 PM

    I'm thinking.
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #12

    Feb 25, 2010, 06:29 PM
    Quote Originally Posted by hkstroud View Post
    I'm thinking.
    w/ the switch off, the two spun together black wires and the three spun together red wired have 120 volts
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #13

    Feb 25, 2010, 06:31 PM
    Quote Originally Posted by hkstroud View Post
    I'm thinking.
    w/ the switch turned on and the dimmer all the way up, the two spun together black wires have 120 volts but no others
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #14

    Feb 25, 2010, 06:37 PM
    Are the two red connect to anything?
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #15

    Feb 25, 2010, 06:43 PM
    Quote Originally Posted by hkstroud View Post
    Are the two red connect to anything?
    At the switch box, one of the blacks from one of the dimmers and one of the blacks from the other dimmer join together in a butt connector w/ a red from one romex, a red from another romex, and a black from another romex. At the box on the ceiling, the two reds come out spun together.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #16

    Feb 25, 2010, 06:49 PM

    Having a little trouble accounting for all the cables in the switch box.
    At the ceiling box with the switch off, test for voltage between the ground and the single black wire. Should not have any voltage. Then turn switch on and test again.
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #17

    Feb 25, 2010, 06:50 PM
    Quote Originally Posted by hkstroud View Post
    Having a little trouble accounting for all the cables in the switch box.
    At the ceiling box with the switch off, test for voltage between the ground and the single black wire. Should not have any voltage. Then turn switch on and test again.
    No voltage either way
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #18

    Feb 25, 2010, 06:52 PM
    Quote Originally Posted by ctriverboat55 View Post
    no voltage either way
    Scratch that, it has voltage w/ switch on
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #19

    Feb 25, 2010, 06:56 PM

    So you have no voltage with the switch off but do have voltage with the switch on, correct?
    ctriverboat55's Avatar
    ctriverboat55 Posts: 12, Reputation: 1
    New Member
     
    #20

    Feb 25, 2010, 07:02 PM
    Quote Originally Posted by hkstroud View Post
    So you have no voltage with the switch off but do have voltage with the switch on, correct?
    Correct

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a light remote, light has 2 wires, remote has 3, need wiring diagram [ 7 Answers ]

I am wiring a light remote control, light has 2 wires (black and white), remote has 3 wires (black, white, and blue) not sure how to hook up the blue wire

Stuck wiring ceiling fan to existing light switch. [ 17 Answers ]

Attempting to wire a ceiling fan to an existing light switch. Ceiling fan has Black, Blue (light), white and ground. Fan being installed is light adaptable, but will have absolutely no plans of adding the light. I have run 14-2 wire to the light switch. Light switch has Black, Red, White and...

Connecting two wires from light kit pull chain switch 2 wire to light kit for fan [ 6 Answers ]

I would like advise on how to attach the two black wires on the light kit pull chain switch to the light kit on the ceiling fan. I see there are two unattached wires on the light kit, one is black and the other is white. Are these the correct wires to attach the pull chain to? If so, how do I...

Wiring 4 wire outlet w/only 3 wires [ 11 Answers ]

My wall outlet is a 3 prong and I want to convert it to a 4 prong but I only have three wires? Should I make a jumper in the outlet from the common to the 4th grounding outlet?

How to wire an additional light to an existing 3-way light switch [ 5 Answers ]

I am in the process of finishing my basement, and the light at the top of the stairs is connected to a light switch at the top and bottom of the stairwell. I would like to add another light to this configuration at the bottom of the stairs. From what I can see, the power runs into the light...


View more questions Search